georgestolz said:
I'd be careful about posting jokes without making that clear, as it only contributes to people's misunderstanding of grounding and bonding.
YES, SIR! SORRY, SIR! IT WON"T HAPPEN AGAIN, SIR! [size=-2](not)[/size]
"Second, a ground rod at a resistance to earth of 25 ohms is a high resistance."
No, it's not. It's not unheard of to have a ground rod at as much as ten times that resistance to ground or more.
"So high it is actually the max permitted by code without augmentation."
You assume that the CMP's reasoning behind the requirement is that they consider that value to be "high." That remains to be seen. I have not seen any evidence one way or another regarding their reasoning behind the requirement.
I was speaking [writing] in terms of functionality as implied by
code. You are correct in that a ground round may have a resistance many times the implied target value... and as I stated, code requires when this is the case with a sole [system?] electrode, it must be augmented. (Is there an echo in here?) You say ta-may-toe, I say tuh-mah-toe...
"Both of you are probably assuming a breaker trip rating of 15 amps or higher... again, this is a typical situation, but not all encompassing. In some of the industrial situations I have been involved with, I have encountered CB's having a trip rating of less than 1 amp."
That is irrelevant - the earth is never an acceptable ground fault current path.
That's exactly right. As I see it, the installation as depicted is in violation by not being bonded to service ground!!!
If the circuit in the image was on that breaker, it most likely would have tripped.
It would have tripped when the ballast of that pole was energized, regardless of a fault condition.
The remark was only to offer contention to Bob's assertion, "FPE, GE or Square D it does not matter a ground rod will not trip them [circuit breakers]." Nothing more. I tend to interpret in "many shades of gray". IMO, you guys are little too "black and white".
...and you continue to make assumptions. In all likelihood, you are correct in there being an HID ballast connected atop the pictured pole. Nevertheless, it is an assumption. Since you assume the load is an HID ballast, I'm going to assume it is a low current sensor of some sort, for the L of it
Regardless, the one thing I want to make plainly evident here is: Assumptions in this profession can get you killed!
"The misconception is on the part of the reader, extracting more information than what was stated. Let me clarify. I said electricity 'seeks' the path of least resistance."
I read what you wrote. Writing it a second time doesn't make it any more correct, and you are doing a disservice to the apprentices and students who visit this forum for accurate information. It is a falsehood. It is incorrect. It is misleading. It doesn't merit defense; the statement only serves to confuse and misinform.
"I did not say electricity does not utilize all available paths."
That is a profound omission!
Again, that is exactly correct. I'm a profound person and I can not, will not change my disposition to suite your's or anyone's desires or requirements. In the interest mutual respect, I will attempt to "bend" a bit, but that's the best I can offer. Nonetheless, you need to be aware I'm not going to rewrite "the book" for every comment I make.
Let's change your "correct comment" to be fully correct: Electricity...utilizes all available paths inversely proportional to the resistances encountered in achieving or attempting to return to it's source.
You can change my words any way you want if it makes you feel better. Do you feel better now?
So, I guess the rod is the answer after all. But it's not very comforting, IMO.
I forgot to mention that I am among those of the contention a ground rod is required.
FWIW, I've been on hiatus from citing code longer than you've been in the trade.
On that note...
Grounding conductors are intended to have zero current---oh, oh, let me correct that---no objectionable current. As I suggested, a simple test will provide the answer. If in all likelihood, objectionable current will result, so enlighten yourselves with with 250.6(A, B)... but then I have to ask how is it possible to meet the requirements of 250.4(A)(5) or (B)(4) in persuing alteration 250.6(B)(3)?