1960's Motel pool.
Pump / pool building, pool panel & pool across parking lot.
Pool panel fed with 10/2 from across the parking lot NO NEUTRAL, 2 hots and ground.
No pool lights.
Has metal ladders for pool access.
No bonding loop.
Concrete pool.
Ground in feed seems compromised. They called and said the 240v pump works but not the 120v lights on the patio. I told my guys to go cut the power so it can't be reconnected easily.
How do I make this safe? It will have its own meter soon (1 month+ waiting on power company), but still no bonding loop. Might check for rebar with big hammer in the future if required. Nothing visible.
How do I make it safe right now?
My plan until there is a new service.
1 - drive a ground rod
2 - run ground wire to pool panel and pump from ground rod
3 - swap pool pump breaker to GFCI
4 - repair or replace pool panel feed from motel and ensure it has a ground wire back to feeding panel.
5 - if replacing wire add a ground bar and neutral wire from feeding panel in motel?
Appreciate any help. I hate pool work.
Pump / pool building, pool panel & pool across parking lot.
Pool panel fed with 10/2 from across the parking lot NO NEUTRAL, 2 hots and ground.
No pool lights.
Has metal ladders for pool access.
No bonding loop.
Concrete pool.
Ground in feed seems compromised. They called and said the 240v pump works but not the 120v lights on the patio. I told my guys to go cut the power so it can't be reconnected easily.
How do I make this safe? It will have its own meter soon (1 month+ waiting on power company), but still no bonding loop. Might check for rebar with big hammer in the future if required. Nothing visible.
How do I make it safe right now?
My plan until there is a new service.
1 - drive a ground rod
2 - run ground wire to pool panel and pump from ground rod
3 - swap pool pump breaker to GFCI
4 - repair or replace pool panel feed from motel and ensure it has a ground wire back to feeding panel.
5 - if replacing wire add a ground bar and neutral wire from feeding panel in motel?
Appreciate any help. I hate pool work.