Fulthrotl
~Autocorrect is My Worst Enema.~
- Occupation
- E
Don't splices have to be accessible?
hypress, and 3m coldshrink in direct burial isn't accessible, but is done.
i'd megger all of the conductors, PH2PH and PH2GND, and repull the damaged one.
Don't splices have to be accessible?
One of the sales pitches were that splices made with a compression tool had less resistance than the wire itself. The one time I measured and compared the voltage drop on a section wire, they were correct.
I find that hard to believe, unless the connector made of a material of less resistance than the conductor being spliced, but even then won't lessen overall resistance of the completed assembly if it is only a small section involved in the splicing method.
Splice 10 feet of gold into a length of copper, and you first have a very expensive splice, but may also noticeably reduce the resistance of the overall length.
I found it hard to believe myself but then I had all the necessary components of a scientific experiment right there. :roll: So I tried it.
I took the measurment on a piece of the bare acsr overhead we had spliced. I cleaned the conductor on both sides of the splice and on an equal distance of the original. I believe it was an Amprobe AM4 digital meter. The current was constant and I repeated the readings several times. Each was lower. Close enough