Here is the 09 70E.

120.2 Deenergized Electrical Conductors or Circuit Parts That Have Lockout/Tagout Devices Applied

120.2(F)(1)(a)Locating Sources.

Up-to-date single-line drawings shall be considered a primary reference source for such information.
One lines are also referenced in a round about way in 70E 120.2(B)(3).
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Here is the 09 70E.

One lines are also referenced in a round about way in 70E 120.2(B)(3).
Maybe I should have said strongly recommended.

What does the one-line of a single panel installation look like?
A one-line showing only the LOTO points (and no other information) would suffice for the OSHA reference.
 