Open Snap-in bushings

Status
Not open for further replies.
As many as you can squeeze in. Will depend on the cable conductor size and number of conductors in each cable.
 
Hopefully you are planning to use those to pass through a metal stud or similar and not to enter a box/enclosure.
I had a local AHJ inspector call me for a reference in NEC because one of their junior inspectors was calling out these crammed packed going into a sub-panel. I couldn't recall any NEC section expect finding a means of securing them. I referred them to the manufacture of the bushing to see if they had a listing, turned up nothing. Any help on this pointing the inspectors (AHJ) to a code would be great so I can pass it along. I laughed when I heard what they were calling as we segregate them out with NM-B clamps. These EC's I guess are out of towners low balling local EC's.
 
I had a local AHJ inspector call me for a reference in NEC because one of their junior inspectors was calling out these crammed packed going into a sub-panel. I couldn't recall any NEC section expect finding a means of securing them. I referred them to the manufacture of the bushing to see if they had a listing, turned up nothing. Any help on this pointing the inspectors (AHJ) to a code would be great so I can pass it along. I laughed when I heard what they were calling as we segregate them out with NM-B clamps. These EC's I guess are out of towners low balling local EC's.
312.5(C) would prohibit using those as the point of entry into a panel.
 
May be confusing these with Raco 4714.

They look similar but the Raco product is listed as an NM connector.
 