In Mike’s video did he say that they floated the equipotential bonding grid? How would they have done that?
But even if you float the equipotential bond and apply 120 V to the water as they did ,
there’s still two potential hazards.
It was not at all clear to me what circumstances were arranged and then what they what they wanted to specifically demonstrate. I can only guess, and that was one of the reasons I would suggest the mouse test. It is pretty easy to go through several variations of swimmable with voltage, the bird on a wire scenario, and then deceased mice from the same experiment with different and kind of obscure but lethal changes.
I started watching the video at about the 50 minute mark as originally posted so I don't know what was shown or discussed prior. I am assuming the pump is usually connected with plastic plumbing so it could have an EGC but then they were claiming the water was at 120, I believe with no wire dropped into it, and the intent was to show that with an properly constructed equipotential grid, there would exist no potential voltage difference within the grid coverage area.
From what was shown, I believe what they did was to float the grid meaning, disconnect it from the supply EGC, and then connect the supply 120 to the grid, so the grid itself (and the water) was at 120 to remote earth. And then Mike went swimming in it, apparently demonstrating no potential voltage difference within the water because of the effectiveness of the equipotential grid. I don't know and don't want to speak for him.
1st, If there was a utility stud pole nearby it would have a ground rod and a solid conductor attached to the primary neutral. The 120 V in the water could flow through Mike and try to return to the source of the utility stud pole to the primary neutral. Of course the soil would have to be damp enough to be conductive from the pool shell all the way back to the stud pole primary neutral.
Yes absolutely there was a lot more going on. If or with the grid at 120 and also if the Voltage supply was also connected to earth (by the system bonding jumper), the resistance of the Earth would have completed that circuit and shown significant current flow. They made reference to this somewhere, talking about a 24 ga wire that melted and blew up like a fuse. I would have really wanted to see a clamp on Ampmeter on the system bonding jumper, which would give a very eye opening reading. I would have to watch again from the beginning to see what they were trying to show.
2nd , The equipment grounding conductor & the equipotential bonding system is bonded together at the pool pump. When 120 V is applied to the water it’ll go through Mike , through the equipotential, onto the casing of the pool pump motor, to the equipment grounding conductor in the motor, to the pool panel, and back to the service equipment, back to the utility transformer primary neutral.
The voltage always wants to go back to the source.
Sent from my iPhone using Tapatalk
Again I don't know and did not watch the entirety. With everything connected normally, applying voltage anywere with cause current to flow, there exists "an effective fault (clearing) current path", sufficient to trip the upstream protective device. At one point they talked about seeing 90 Amps and the soffit light fixtures caught fire because (that was the fault current clearing path after they had disconnected the others). I believe they had floated the grid at that point or that would have carried the fault current.
If they had floated the supply voltage at the system bonding jumper, (which may have been at the Utility transformer and inaccessible to them), the system would only reference to ground at the first ground fault (that they created). With a system earthed somewhere but at a remote point, there was step potential Voltage everywhere, which appears to be the actual, and they may have floated the grid and then raised it to 120 (then Mike goes swimming in it).
In the video, I did see what looked like a green #10 or so (THWN) taped to the patio paver tiles and I am guessing that was the temporary connected EGC reference ground. Touching that may have been instantly lethal. He was standing and reaching within 2 ft of it.