The one thing I love most about this discussion forum is the way a lot of folks will debate the verbiage of the code stating, ?show me text? when they need to but at other times make the statement that the verbiage as it is written is not what is there.
This is one such case but I think those who are looking for the verbiage is simply overlooking what is written.
(7) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts shall be bonded.
Exception No. 1: Those separated from the pool by a permanent barrier shall not be required to be bonded.
Exception No. 2: Those greater than 1.5 m (5 ft) horizontally of the inside walls of the pool shall not be required to be bonded.
Exception No. 3: Those greater than 3.7 m (12 ft) measured vertically above the maximum water level of the pool, or as measured vertically above any observation stands, towers, or platforms, or any diving structures, shall not be required to be bonded.
Here in this section there are many different items that are being addressed. As outlined in the header it is addressing metal wiring methods as well as equipment. In the text is mentions metal sheathed cable and it also mentions raceways. Now most of us are smart enough to know there is no need to bond a nonmetallic raceway so they must be talking about metallic raceways.
In the title it also mentions ?and equipment? which would lead most to think of something other than electrical wiring methods. Several times the code mentions metal piping and 250.104 is one of great debate. This metal piping as outlined here could be metal water piping, metal gas piping or any other metal piping one could think of.
All fixed metal parts has nothing stated that would lead me to believe that these fix metal parts have anything to do with the electrical system supplying the pool the verbiage does lead some to believe that any fixed metal fitting such as a metal door mounted in a wooded frame that could be bonded through the hinge.