I know this has been beat to a pulp but I have to raise the issue one more time.
We all have opinions as to what the code says or what the code means but, I think we should also look at what the code intends. In a recent "Code Quandries" article in EC & M Magazine Mike Holt showed an illustration where a drill, plugged into an outdoor receptacle with a w/p flap cover would not meet code. While I hate to disagree with the master I have to take exception to his interpretation.
Section 406.8(B)(1) indicates that outdoor receptacles have to have an enclosure that is weatherproof whether an attachment plug is installed or not. That doesn't mean that you have to anticipate that somewhere down the line a homeowner might have a tool or appliance plugged in all year 'round and you should have installed a bubble cover to cover this possibility. The gasketing for the bubble cover doesn't offer any more protection than the gasketing for a flap cover.
If you read the article further to section 406.8(B)(2)(a) & (b) it explains the difference between intended-not attended and intended-attended. What I believe paragraph (B)(1) intends is that you should install a weatherproof cover based on guidelines of (2)(a) & (b) and not the indoor cover usually supplied with the GFI receptacle. If you know that a landscape lighting transformer is going to be plugged into a receptacle, then that GFI receptacle should have a bubble cover. If it's a general purpose receptacle, a flap cover is acceptable
OK. I'm off the soap box !!!
We all have opinions as to what the code says or what the code means but, I think we should also look at what the code intends. In a recent "Code Quandries" article in EC & M Magazine Mike Holt showed an illustration where a drill, plugged into an outdoor receptacle with a w/p flap cover would not meet code. While I hate to disagree with the master I have to take exception to his interpretation.
Section 406.8(B)(1) indicates that outdoor receptacles have to have an enclosure that is weatherproof whether an attachment plug is installed or not. That doesn't mean that you have to anticipate that somewhere down the line a homeowner might have a tool or appliance plugged in all year 'round and you should have installed a bubble cover to cover this possibility. The gasketing for the bubble cover doesn't offer any more protection than the gasketing for a flap cover.
If you read the article further to section 406.8(B)(2)(a) & (b) it explains the difference between intended-not attended and intended-attended. What I believe paragraph (B)(1) intends is that you should install a weatherproof cover based on guidelines of (2)(a) & (b) and not the indoor cover usually supplied with the GFI receptacle. If you know that a landscape lighting transformer is going to be plugged into a receptacle, then that GFI receptacle should have a bubble cover. If it's a general purpose receptacle, a flap cover is acceptable
OK. I'm off the soap box !!!