Re: Outlets Per Breaker
physis,
Branch circuits,art.210.11, provides the circuits to the loads computed in 22o.3 more so 220.3(b)(9), which is the 180va per duplex recpt. you use to figure load calcs.
I asked to explain 220.13, because it states that if you use the 180va computation you are allowed to add it to the lighting load and then use demand factors! The first 10000va at 100% over that only 50%, so now I can put 20 duplex on a 15a and 26 on a 20a c.b. Physis, I'm only doing this because you hear it all the time "You can only put ?# of recpts. on a circuit". It's not code,It's misunderstood.
frank