Re: Outlets Per Breaker
The question:
Yes.
From 220.3 Computation of Branch Circuit Loads.
This section specifies the power and therefore current that each receptacle will be calculated to require.
But this section does.
For 120v, 180w/120v = 1.5a.
15a/1.5a = 10
20a/1.5a = 13.3
__________________________________________________________________________________
Frank, addressing 220.13.
It is part of Part II of Article 220.
[ May 04, 2005, 02:30 PM: Message edited by: physis ]
The question:
Answering for receptacles in nondwelling units from the 2002 NEC:Is there a code limit on the number of outlets allowed per breaker?
Yes.
It does not require that a branch circuit be installed to supply the calculated current.220.3(B)(9) Receptacle Outlets........... receptacle outlets shall be computed at not less than 180 volt-amperes for each single or for each multiple receptacle on one yoke....................
That is quite simply the end of the story. All that is left is to do the math.210.11 Branch Circuits Required. Branch circuits for lighting and for appliances, including motor operated appliances, shall be provided to supply the loads computed in accordance with 220.3......................
15a/1.5a = 10
20a/1.5a = 13.3
There is no allowance to apply a demand factor to a branch circuit.II Feeders and Services
220.10 General. The computed load of a feeder or service shall not be less than the sum of the loads on the branch circuits supplied, as determined by Part I of this article, after any applicable demand factors permitted by Parts II, III or IV have been applied.