hurk27
- Portage, Indiana NEC: 2008
Re: Outlets Per Breaker
Actually George The statement "dedicated" is kind of a loose term we use as a way of describing a single circuit that only supply's certain items. It could serve one single receptacle outlet. or several that just feed a group of certain appliances. To not be a dedicated circuit would be more like the circuits that feed GP receptacles or receptacles and lights.
We dedicate one circuit per GFCI in the kitchen even though the GFCI also feeds a couple other receptacles but to us it is still a dedicated circuit.
We also have a dedicated circuit that feeds the laundry receptacle which is a duplex so the dryer can be plugged in.
But as far as the refrigerator goes having a 15 amp duplex on a 20 amp circuit behind it is not a NEC issue as the refrigerator is not required to be on a single receptacle. If you had a disposal that pulled more than the 50% allowed by 210.23(A)(2) then I could see your point, but a refrigerator is not a fixed in place appliance and does not have a 20 amp cord on it, and does not pull more than 80% of the circuit as required in 210.23(A)(1) Maybe a Subzero might?
Here is my view:
The NEC only requires a single receptacle to have the rating of the circuit.
Where two or more receptacles are suppled by a 20 amp circuit it is allowed to use a 15 amp rated receptacle.
A duplex is two receptacles as per the definition in the NEC.
A refrigerator is not a fixed in place appliance so it only needs to be less than the 80% of the circuit feeding it.
So a refrigerator is not required to be on a dedicated circuit, thus not requiring a single receptacle.
There clear as mud!
Here is my view:
There clear as mud!