wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Customer's installation was a code violation before you got there. Customer will need to hire you to run a new circuit.the existing circuit is not SEU. It is 8-2 romex.
Cheers, Wayne
Customer's installation was a code violation before you got there. Customer will need to hire you to run a new circuit.the existing circuit is not SEU. It is 8-2 romex.
I said you may.I've installed tons of ranges & ovens covering most brands. All of them have instructions for 3 and 4-wire. Never saw one that said you must run a 4-wire circuit if you only have a 3 wire.
Well,Appliance Tech here. I still see a lot of 3 wire installs. As far as I know, All can be either L1,L2 and N OR. L1, L2, N, and Ground>
SE cable is used, among other uses, as service entrance wire. The bare conductor is the grounded/neutral conductor. NM cable isn't service entrance cable. The bare conductor is the EGC. The white conductor can be used as a grounded/neutral conductor or an ungrounded conductor if re-identified. In a nutshell, SE bare = grounded/neutral, NM (Romex) bare conductor = EGC. See my post #22 for more info.My question is, what is the difference between a bare stranded wire in an SE cable and a bare copper wire in an 8-2 romex cable ? Why is SE allowed but not NM cable ? Thank you
Prior to the adoption of the 1996 NEC which can lag by a number of years.Section 250-140 (Section 250-60 in the 1996
NEC® and previous editions of the NEC®) now
applies only to existing branch-circuit installations.
For those installations wired according to the rules of
Section 250-60 prior to the 1996 NEC,® the required
appliance grounding was accomplished by the small
copper bonding strap furnished by the appliance
manufacturer that connected between the neutral terminal
and the metal frame of the appliance.
This method was used only in older homes prior to NEC 1996.
thank you for your time, you all have helped me many times. I'm not trying to drag this question on. But I wonder why SE is ok by NEC and NM is not....it seems like a bare wire is a bare wire...whichever cable it is in. Is it because SE usually wraps around the other conductors in the sheath to affect inductance or something like that ? Just curious, and thank you again for showing me the NEC references.SE cable is used, among other uses, as service entrance wire. The bare conductor is the grounded/neutral conductor. NM cable isn't service entrance cable. The bare conductor is the EGC. The white conductor can be used as a grounded/neutral conductor or an ungrounded conductor if re-identified. In a nutshell, SE bare = grounded/neutral, NM (Romex) bare conductor = EGC. See my post #22 for more info.
I think the bare conductor in NM is strictly sized per 250.122 the bare conductor in SE cable might be typically larger.thank you for your time, you all have helped me many times. I'm not trying to drag this question on. But I wonder why SE is ok by NEC and NM is not.
The motor, timer, and drum light if present, in a dryer are all 120V, sometimes I wonder if we had 240V instead of 120V as the normal voltage how much better off we would have been.I think the bare conductor in NM is strictly sized per 250.122 the bare conductor in SE cable might be typically larger.
The question we should all be asking is why in the world is any electric cooking appliance still using a neutral to power what a light and a clock?
They certainly never use the neutral for the cooking load.
The 3rd wire in older dryers was an EGC. With the advent of digital displays in new dryers a neutral is needed. Hooking up the EGC and using it as a neutral is a Code violation.The third wire in your existing branch circuit is a grounded conductor, not an equipment grounding conductor.
Mark
The third wire in old dryers was a neutral for the dryer motor.The 3rd wire in older dryers was an EGC. With the advent of digital displays in new dryers a neutral is needed. Hooking up the EGC and using it as a neutral is a Code violation...
Correct, as far as I know, only the heating element in dryers needed the 240V.The third wire in old dryers was a neutral for the dryer motor.
I think it's entirely historical reasons, with little or no technical basis.But I wonder why SE is ok by NEC and NM is not.
I'll take yours and Little Bills word for it. Seems to me that a bare wire (i.e. that of an SE cable) would be (or should have been) a Code violation. Maybe the CMP's at the time thought it would be OK because the jacket of the SE cable would suffice as insulation and that it had to originate from the main breaker panel.The third wire in old dryers was a neutral for the dryer motor.
Allot of the old 3 wire SE cable ranges I see around here are 8-8-8 SE cable. ( the bare braid equals #8)I think it's entirely historical reasons, with little or no technical basis.
Cheers, Wayne


Though when dealing with a dryer, you can run 10-3 no ground, but can't run 10-2/WG even though all conductors are 10 AWG in either case, and probably would be with SE cable if you can find any. Have seen old SE cable in sizes that small but all were from ~1950 or earlier.I think the bare conductor in NM is strictly sized per 250.122 the bare conductor in SE cable might be typically larger.
The question we should all be asking is why in the world is any electric cooking appliance still using a neutral to power what a light and a clock?
They certainly never use the neutral for the cooking load.