Oven Wire Size Question

Merry Christmas

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
I suppose its all in how you interpret 'one wall-mounted oven. To me its a double oven but it is a single wall mounted appliance so yeah I'd say to be safe your right 50A circuit.
I shoot for 6666 ser for things like this it's just easier. If worried about the copper only conductors then hit a 4 11/16 in cabinet and use splice reducers to 6in copper then the leads but I've never worried if using splice reducers or dual rated split bolts
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I shoot for 6666 ser for things like this it's just easier. If worried about the copper only conductors then hit a 4 11/16 in cabinet and use splice reducers to 6in copper then the leads but I've never worried if using splice reducers or dual rated split bolts
Why would you pull a #6 equipment grounding conductor? Do they even make 6-6-6-6 ser? I guess for a 3 phase service of 60 amps????
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Simple, it's wrong. It does say that you need to follow the code so you can ignore their mistake. This is similar to a recent thread about how poor instructions can be.
This was the point that I brought up before. The NEC requires manufacture instructions to be followed and takes priority over NEC general instructions. Whose fault would the electrical inspector likely pin for this, if this setup resulted in an insulation fire? Especially the installer running 10 AWG wire on a 50i breaker according to manufacture listed instructions?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This was the point that I brought up before. The NEC requires manufacture instructions to be followed and takes priority over NEC general instructions. Whose fault would the electrical inspector likely pin for this, if this setup resulted in an insulation fire? Especially the installer running 10 AWG wire on a 50i breaker according to manufacture listed instructions?
IMO no good inspector is going to let the installer follow those instructions when then directly contradict the NEC requirements.
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
This was the point that I brought up before. The NEC requires manufacture instructions to be followed and takes priority over NEC general instructions. Whose fault would the electrical inspector likely pin for this, if this setup resulted in an insulation fire? Especially the installer running 10 AWG wire on a 50i breaker according to manufacture listed instructions?

If you followed the mistaken instructions, and put that setup on 10 AWG, the wire would never even get warm.

Still wrong, but it would work.
 

NoahsArc

Senior Member
Location
Illinois
Occupation
Residential EC
since locally we only do gas.
Speak of the damned devil. Good thing I just did my homework. Love how that works out sometimes. (this guy has a gas line in the pic he sent me, I don't get it at all)
I've got an 11.4kw range -> 220.55 -> 8kW -> 34A -> 40A minimum. 2x #8 and a #10 THHN neutral sounds gtg
According to note 4 that demand factor only applies to a range.
"for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating.... load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit.... add the ratings as equivalent to one range."
I don't see a clear distinction there.

@SteveO28 what pricing did you settle on?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Installing a double oven for a new kitchen. LG WDEP9427. Install manual says it requires a 50amp breaker with 10g wire. Oven draws 42.5 amps. I planned on running a 6awg based on 42.5x1.25= 53.125a. Anyone want to fill me in why the manual calls for 10s?
This is a case where the NRTL should be notified so they can have corrections made in the docs. As mentioned here and in the previous post about this, in my view this is a chronic problem with all the NRTLs.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't see a clear distinction there.
Here is the entire note, there is a distinction between a range and a wall mounted oven. The range can use the demand factor in Note #4 of T220.55, second sentence. The wall mounted oven uses the KW rating (third sentence) to determine the branch circuit size without the demand factor.

Note 4.
Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch-circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance. The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to one range.
 

NoahsArc

Senior Member
Location
Illinois
Occupation
Residential EC
For whatever reason now I see it, despite reading the same thing both times. I think italics was the issue.. not me.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Here is the entire note, there is a distinction between a range and a wall mounted oven. The range can use the demand factor in Note #4 of T220.55, second sentence. The wall mounted oven uses the KW rating (third sentence) to determine the branch circuit size without the demand factor.
As a devil's advocate, I will observe that there are 1,800W counter-mounted cooking units available, such as:


Therefore it should be permissible to use an 1,800W allowance for a counter-mounted cooking unit in applying T220.55. The double oven is 10,700W, plus the 1,800W allowance makes 12.5 kW. So the Column C rating is 8 kW * 1.05 = 8.4 kW = 35A @ 240V. [Same calculation would apply for up to a 2,700W allowance for the cooktop, if 0.4 kW is not a "major fraction" of a kW.]

This line of thought would permit a 35A branch circuit with 35A OCPD.

Cheers, Wayne
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As a devil's advocate, I will observe that there are 1,800W counter-mounted cooking units available, such as:


Therefore it should be permissible to use an 1,800W allowance for a counter-mounted cooking unit in applying T220.55. The double oven is 10,700W, plus the 1,800W allowance makes 12.5 kW. So the Column C rating is 8 kW * 1.05 = 8.4 kW = 35A @ 240V. [Same calculation would apply for up to a 2,700W allowance for the cooktop, if 0.4 kW is not a "major fraction" of a kW.]

This line of thought would permit a 35A branch circuit with 35A OCPD.

Cheers, Wayne
I'm confused, is there a counter mounted unit in the OP's question or are you just outlining other possible scenarios?
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
I'm confused, is there a counter mounted unit in the OP's question or are you just outlining other possible scenarios?
I think he is using it like the apartment electric kitchen calculation which leads to a lower number even if the apt is using gas cooking.

Same deal here, add a phantom cooktop and you get a lower number than just the oven by itself.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
This was the point that I brought up before. The NEC requires manufacture instructions to be followed and takes priority over NEC general instructions. Whose fault would the electrical inspector likely pin for this, if this setup resulted in an insulation fire? Especially the installer running 10 AWG wire on a 50i breaker according to manufacture listed instructions?
IMO no good inspector is going to let the installer follow those instructions when then directly contradict the NEC requirements.
This is a case where the NRTL should be notified so they can have corrections made in the docs. As mentioned here and in the previous post about this, in my view this is a chronic problem with all the NRTLs.

As I read this I got to wondering..
So I did a thing. Just got this response:
IMG_4252.jpeg
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
So the way I personally reconcile code / instruction discrepancies is that they are code must be followed but instructions also must be so either a product is incompatible with a wiring method or location or it gets an above and beyond install.

Fridge says don't gfi well if in a location that requires gfi then the fridge is the wrong fridge.

Non damp rated light in a damp area then wrong light

Fitting says listed for 10 cables and nothing in code prohibits it then no issue till someone tries to use the wrong cable combinations or in a location other than what's in the instructions
 

brycenesbitt

Senior Member
Location
United States
Ovens use the 240V or 208V circuit to power the Watt-intensive heating elements, and the 120V circuit to power the fan and controls. This means the amount of current on the neutral is small compared to the amount on the live wires.
Looks like this one puts 0A on the neutral,
at least based on the European version of the same model.
 