I was disagreeing with the last paragraph of your post #46.@ Besoeker... I get your point about eff'y, competition, guarantee, etc, but ur sophisticated model doesn't explain PtonSparky's situation!
I was disagreeing with the last paragraph of your post #46.@ Besoeker... I get your point about eff'y, competition, guarantee, etc, but ur sophisticated model doesn't explain PtonSparky's situation!
So you want a high slip like a design D? Those might be used in oil fields but I would think a standard pump would have a design B.@ Mivey... Thanks for the intent! But, the data you proposed doesn't come close to the values necessary explain PtonSparky's situation!
May not be noticeable at the measuring point.However, a PFC installation usually results in some kW reduction!
Small feeder losses, capacitors producing heat, inductive heating on mis-wired circuit, etc. Not sure you can tie it to the motor but please proceed.PtonSparky's case piqued my interest because while a substantial line-current change occurred, the expected kW change didn't! So that led to this "investigation!"
Phil
The voltage drop caused by lagging reactive current component of the motor load current in the supply leads to the motor is compensated by the capacitor across the motor terminals and that much voltage improvement would happen to the motor terminal voltage.
Honestly, I don't think there's much VD in there is the system was designed properly.
Small feeder losses, capacitors producing heat, inductive heating on mis-wired circuit, etc. Not sure you can tie it to the motor but please proceed.
Do some wiring on farms and you learn when to be precise with voltage drop and when to settle for a little more then you maybe would inside an industrial plant. With irrigation work we often run anywhere between 1300 to 3000 feet. Then you get the occasional 400 to 800 foot run and that is nothing when it comes to VD effects.
Power factor correction does help lower VA on such runs which will help with VD.
What gets me is the irrigation companies make these long runs and act surprised when the controller drops out during a motor start. I suggest a UPS or power supply that has a little more flicker withstand and they want to complain about service voltage. It ain't the service voltage, its the secondary voltage regulation problem cause by the long circuit.Do some wiring on farms and you learn when to be precise with voltage drop and when to settle for a little more then you maybe would inside an industrial plant. With irrigation work we often run anywhere between 1300 to 3000 feet. Then you get the occasional 400 to 800 foot run and that is nothing when it comes to VD effects.
Power factor correction does help lower VA on such runs which will help with VD.
Consider a paper mill, for example, which has a large area. There is scope for VD reduction by employing capacitors.You meant to tell me there are still crazy designers out there?
Why run a low voltage supply for about a mile?
Consider a paper mill, for example, which has a large area. There is scope for VD reduction by employing capacitors.
Decide depending on which costs more in the long run.Then I'll have to choose between 1) running MV lines, install load centers to serve the group of low-voltage loads at select locations or 2) run conductors sized to consider the possible voltage drops in your paper mill.
Capacitors are a bit problematic in paper mills.Consider a paper mill, for example, which has a large area. There is scope for VD reduction by employing capacitors.
Like?Capacitors are a bit problematic in paper mills.
Harmonics. I don't know how much you know about paper mills.Like?
You meant to tell me there are still crazy designers out there?
Why run a low voltage supply for about a mile?
Your solution?Harmonics. I don't know how much you know about paper mills.
There are lots of variable speed drives in a paper mill. A typical paper machine may have a drive suite with 15 variable speed drives usually from about 100 kW and upwards.
The harmonic distortion can be considerable. At one mill I measured 15% voltage distortion. That does not sit comfortably with capacitors and they often fail spectacularly. I've seen lots that did.
For what? Poor power factor, voltage drop or harmonics?Your solution?
INDUCTION MOTOR RATED PARAMETERS |