- Connecticut
- Engineer
I think it's sloppy to say it that way. Rather I would say the same OCPD is meeting both the 230 and 215 requirements.
The is no OCPD sizing requirement in 230. The was the point of the original post.
I still disagree 215.3 is for overcurrent protection of a feeder.
Overcurrent protection of a service conductor is covered in 230.90.
Ummm, part VII? I must not be understanding what you are getting at.The is no OCPD sizing requirement in 230. The was the point of the original post.
Reread the original post.
Did several times before I replied before.
The code specifies similar requirements for overcurrent protection for conductors and equipment in:
210.20
215.3
But I can't find any such requirement for service equipment in Article 230 Part VII (or part VI for that matter even that is only for disconnect rating).
There is nothing in Article 230 regarding the overcurrent protection sizing because 215.3 already covers it.
Maybe, possible you took it wrong also.I don't think you have understood what the OP was asking.
There is a lot of repeating of information in the NEC. Go to the raceway articles and the .1 through .100 are often cut/pasted with only minor changes here and there. But it helps to clarify things when you are looking at 344 and realize this applies to RMC, but you are dealing with EMT and you should maybe check 358 to make sure something isn't different there, even though much of the content is similar in each article. Many things are similar in 210, 215 and 230 as well but there are differences.I think what David is saying is that the overcurrent protective device in the main disconnect protects the wiring of the service conductors since the overcurrent protective device is equal to or smaller than the service conductor ampacity.
It will not protect the wiring ahead of the breaker but it will give load protection via the main breaker. Since that is there is no reason to have it again in article 230. I think that is what David is saying.
Of course, that changes when the 6 disconnect rules is used.
I see asking why specific conductor sizing requirements is mentioned in 210, 215 and 230 with pretty much same wording and then pointing out overcurrent protection requirements are nearly the same in 210 and 215 but similar wording seems to be absent in 230 and question basically is why is it that way.
And you have been asked to explain how that covers it. 215 is presumably for feeders not services.Yes, that is what was being asked. This is the answer to the question...
I will agree to the comment that one device can satisfy both service and feeder requirements and does happen quite often.
I gave an example of a service with overcurrent protection suitable for the service conductors, but with feeder taps only on the load side of the service disconnect. Such feeder taps still need an additional overcurrent device at the load end of the tap before 215.3 is satisfied.
Only thing I am seeing in post 15 is the protection of a feeder inherently protects the service conductor - one device fulfills two needs.I gave an example of how it covers it in post #15.
With your example of feeder taps on the load side of the disconnect, it is still Art. 215 which is providing the direction for sizing the main OCPD.
There is no indication in 215.3 or anything in 230 that points back to 215.3 that this is also considered to be service conductor overcurrent protection, it just happens to work out that way most of the time.
And I do agree that taps on load side are feeders and covered by 215, but their overcurrent protection isn't coming from 215.3, it is a special permission in 240.21.
Now technically there is still a feeder before you can tap it, though it may be composed of nothing more than a multiport lug on the switch or breaker and not an art 310 conductor.
What you should see in post 15 is the sizing of the main OCPD based on Art. 215. Said OCPD coverd by 215.3 is for the feeder on the load side of the OCPD and has nothing to do with what is on the supply side of that OCPD.
That isn't the OP's question. I don't see it that way, unless OP states otherwise, I'm sticking with what I have gotten out of it so far.
The sizing of the overcurrent protection for the feeder taps comes from 215.3, not from 240.21. But that is irrelevant to the point I am making.I don't see anything about tap conductors in 215.3. Like I said the feeder may be nothing more than a multiport lug on a switch or breaker.
The overcurrent protection for the feeder that is being tapped is sized 215.3. that I do agree with, once you tap that feeder then you are looking at 240.21 for overcurrent protection limitations on the tap conductor
And mentioning the 210 and 215 and asking about 230 stuff seems to indicate to me he is asking why isn't it the same for service conductors though feeders and branch circuits are almost identically worded, and on top of that mentins the fact that minimum conductor size is almost identical for all three.What's on the supply side of the OCPD is not relevant to the question asked. The question is about the sizing of the OCPD.
Yes they are, but overcurrent protection of the tap involves 240.21 Same tap size and protection could be applied to different sized feeders in some instances, can depend on if 10 or 25 foot tap rule is being used or even if inside/outside.The tap conductors are feeders. 215.2 and 215.3 apply to feeders.
Correct, and tap rules vary according to conditions. Nothing in 215.3 applies to protection of a tap conductor, it applies to the feeder the tap conductor is connected to, the overcurrent protection of the tap is dependent on conditions spelled out in 240.21.215.2 and 215.3 provide the minimum required size of the feeder conductors and the feeder overcurrent protection. 240.21 is "Location in Circuit." 240.21 allows you to provide overcurrent protection to the tap conductors at other than the point they receive their supply, with additional provisions that must be met.