I think what you are missing is how overcurrent protection is looked at,
something to note, 240.4 lets you round up a size for most applications.
another thing to remember is that many overload protection devices are thermal based, so your ocpd could be outdoors in the winter in northern Minnesota while your circuit is inside a foundry.
it's not as precise as other things we deal with, and if used correctly doesn't need to be. usually when there is a problem the overcurrent is not just a little above the circuits rated current, it goes a lot higher. if it is just a little above, there is usually some play in the material/equipment limits and if not everything should still fail safe whether it is a melting wire shorting to a conduit or equipment melting down, the NEC is more of just a minimum fail safe based standard, not a fail without damage.
look at the conductor tables, i'm not sure if you are concerned with protecting equipment or conductors more but look at the tables, they are based on an ambient temperature, the circuits should never have been designed to be expected to be exposed to ambient temperature above what was used for design.
so now consider if your ambient is lower than that then you can run your current above that ambient temp rating, now consider the likelihood of the overcurrent situation happening during the times of the higher ambient temp, some situations it will be very likely some not.
do you really want a code book with all that would be required for what you are asking? i don't. we slightly overbuild in some situations to simplify the design phase, the code gives provisions to allow under engineer supervision to use a calculation to value engineer a conductor size if you don't want to use the dumb tables and corrections like the rest of us
its a dumbed down code yeah, but 80% of the industry still can't apply it properly, so........
there is a listing standard for a ocpd to be able to be rated at a ocpd rating it has to be within a trip curve, so you would have to check the manufacturers trip curves but i would guess the device being looked at that the slowest curve is within the allowable curve for the devices ocpd rating
and i don't have my codebook with me but i think it is over 1KA that a relay engineer has to decide on the curves
something to note, 240.4 lets you round up a size for most applications.
another thing to remember is that many overload protection devices are thermal based, so your ocpd could be outdoors in the winter in northern Minnesota while your circuit is inside a foundry.
it's not as precise as other things we deal with, and if used correctly doesn't need to be. usually when there is a problem the overcurrent is not just a little above the circuits rated current, it goes a lot higher. if it is just a little above, there is usually some play in the material/equipment limits and if not everything should still fail safe whether it is a melting wire shorting to a conduit or equipment melting down, the NEC is more of just a minimum fail safe based standard, not a fail without damage.
look at the conductor tables, i'm not sure if you are concerned with protecting equipment or conductors more but look at the tables, they are based on an ambient temperature, the circuits should never have been designed to be expected to be exposed to ambient temperature above what was used for design.
so now consider if your ambient is lower than that then you can run your current above that ambient temp rating, now consider the likelihood of the overcurrent situation happening during the times of the higher ambient temp, some situations it will be very likely some not.
do you really want a code book with all that would be required for what you are asking? i don't. we slightly overbuild in some situations to simplify the design phase, the code gives provisions to allow under engineer supervision to use a calculation to value engineer a conductor size if you don't want to use the dumb tables and corrections like the rest of us
its a dumbed down code yeah, but 80% of the industry still can't apply it properly, so........
there is a listing standard for a ocpd to be able to be rated at a ocpd rating it has to be within a trip curve, so you would have to check the manufacturers trip curves but i would guess the device being looked at that the slowest curve is within the allowable curve for the devices ocpd rating
and i don't have my codebook with me but i think it is over 1KA that a relay engineer has to decide on the curves