Are there instances where the NEC requires overcurrent protection but doesn’t require the devices to be listed?

There are instances where some of the three characteristics would actually fail to open the protective device for faults. Think about long distribution lines, high impedance faults, and systems with lower ground fault current than the load such as impedance grounded and ungrounded systems.





Sent from my iPhone using Tapatalk

If they failed to open due to those and there was a requirement for the protection then the devices were oversized.
What code requirement are you looking at which you think we would have a problem with that? I'm not extremely familiar with nesc I have a copy though if the problem you are referring to is in there, is there a ground fault requirement?
I believe the basis of your comment is only on ground faults right?
If its high impedance fault you're using to discuss overcurrent or short circuit, then the ocpd would open if not oversized and there was a overload or short circuit, excessive line impedance could very well make what looks like a short circuit actually be just the equivalent of using the wires to contribute to global warming, it's not a short circuit or circuit overload
 
Last edited:
...Stop thinking of LSIG only as a trip-unit feature! ......

No
It would be rare that it wouldn't be (in the context of normal peer group conversation)

... I just provided two simple examples: dual-element fuses and thermal-magnetic breakers. These are certainly not rare and do not use trip-units nor do “many” other single/multi function protection elements in existence. LSIG doesn’t have to be an adjustable trip-unit feature. Again it’s a curve characteristic/parameter... for protective elements.

No you didn't. Any peer group discussion I have been part of would consider the term "LSI" or "LSIG" to indicate an adjustable trip unit. The term T-M (in the context of molded case) would bring to mind the curve I posted earlier. I now understand you wish to attribute A T-M, molded case, non-adjustable to have non-adjustable LT, ST, I characteristics. And a fuse to have non-adjustable LT, ST characteristics. Okay, that's great. I now know that when you say, L, S, I, LS, LSI, LSIG, you could mean a fuse, a standard molded-case, non-adjustable, T-M CB, or an adjustable trip unit. Just have to wait until the context is clear.

And yes, I read Post 1 and Post 5:
"linking LT, ST or I characteristics to the terminology the NEC uses, i.e. Overload, Short-Circuit, Ground-Fault"

"what protection the NEC considers to be adequate when requiring "Overcurrent Protection"; i.e. LT. ST, I, all of these parameters, certain combinations of these parameters, etc."

"The NEC is specific about when GF protection is required but does it say how we may achieve this? For example can I just use short-time and instantaneous if this method is capable of detecting all ground-faults for a particular installation"

I understand you think there should be an NEC correlation between "LT, ST or I" and "Overload, Short-Circuit, Ground-Fault". And, the NEC should be proscriptive about GF protection. Okay, submit your changes. I'm thinking I understand what is required, and what is intended. And they are design issues. The NEC tends to not be prescriptive. Yes, there are parts that are, 250 is an example of a section that is proscriptive. I am generally in favor of the NEC staying out of the design business.
 
... I apologize if I have offended anyone. I’m not intentionally trying to be abrasive as much as I am trying to sift through all the noise.
You fooled me. I was sure you wanted all to know you were the smartest on the block - still am
 
I believe your interpretation is wrong, although I'm not thinking of a good argument against it.

It may be the "over full range" part that may be tripping you up, I don't see how this could mean anything other than the device automatically opening in that range, if it didn't say that you could have a 50 amp breaker that would be able to just trip in the range of say 50 to 1k but still survive 10ka sc, just not trip
This is often the case with MV starters. You do not want the contactor to interrupt current for which it is not rated for so you disable instantaneous and let the fuse take over. Note: The momentary rating of the contactor can still handle the short-circuit, it just cant interrupt it without failing. This is the same for series rated systems. The definition for Overcurrent Protective Device, Branch-Circuit says this range is between its rated current and interrupting rating (not necessarily available short-circuit current).

I don't know of where the NEC discusses the different faults current characteristic's. Nor can I think of where that would be needed.
The definitions for Overcurrent, Overload, and Ground-Fault Protection of Equipment do a very rough job in describing the different fault characteristics (relative magnitude, duration, failure mode). Even though its not enforceable, the informational note to Overcurrent reinforces, "the rules for overcurrent protection are specific for particular situations.". The handbook commentaries provide additional insight as well.

Any of the three st, lt, or I could protect any and all three of those problems (referring to overload, short-circuit and ground-faults)
I'm assuming you deleted post #43 because you realized st, lt, or I couldn't be used to protect any and all three of those problems... For motor applications specifically, its not so much that its impractical, but 430.32(A)(1)/(B)(1), 430.42(D) and 430.51(C)(3) prohibit using only an instantaneous element.

not everything is required to be listed
Can you elaborate on instances where the NEC requires overcurrent protection but doesn’t require the devices to be listed? If one exists, then looking at the listing standards wouldn't help much.

look at the three things we are talking about protecting against, they are problems arising in the electrical system, would either of those three characteristics open the protective device during any of the three types of faults? Yes, they would just take different amounts of time to open
I would maintain no not always. Also, LT can take a many seconds to trip for a short-circuit even though the pick-up setting is where the NEC requires... I doubt just because it will eventually trip you can get away with calling it short-circuit protection.

If they failed to open due to those and there was a requirement for the protection then the devices were oversized.
If you use LT, ST or I elements to detect ground-faults on HRG or ungrounded systems, the breaker would fail to open, not because the protection device was oversized, but because LT, ST, and I are incorrect ways to detect that type of fault. Similarly, for instances where the maximum available short-circuit current is near or less than the load current (as is the case with long distribution lines and high impedance faults), you wouldn't say the protective device is oversized because it didn't trip.

What code requirement are you looking at which you think we would have a problem with that?
None in particular.

I'm not extremely familiar with nesc I have a copy though if the problem you are referring to is in there, is there a ground fault requirement?
Lets stick to NEC.

I believe the basis of your comment is only on ground faults right?
No it's only one random example.

If its high impedance fault you're using to discuss overcurrent or short circuit, then the ocpd would open if not oversized and there was a overload or short circuit, excessive line impedance could very well make what looks like a short circuit actually be just the equivalent of using the wires to contribute to global warming, it's not a short circuit or circuit overload
Without getting into the definition of short-circuit (because the NEC is silent on that one) I think we can all agree a short-circuit is simply an unintentional connection. You don't actually need thousands of amperes to qualify it. Again, if a breaker fails to open in your example, it may have nothing to do with the protection device being oversized.

2017NEC 250.4(A)(5)
What about ground-faults in direct-buried cable, or faults conducted directly to earth? I'm not seeing the Effective Ground-Fault Current Path there.

What NEC year are you using?
2011
 
This is often the case with MV starters. You do not want the contactor to interrupt current for which it is not rated for so you disable instantaneous and let the fuse take over. Note: The momentary rating of the contactor can still handle the short-circuit, it just cant interrupt it without failing. This is the same for series rated systems. The definition for Overcurrent Protective Device, Branch-Circuit says this range is between its rated current and interrupting rating (not necessarily available short-circuit current).
110.9, 240.86

The definitions for Overcurrent, Overload, and Ground-Fault Protection of Equipment do a very rough job in describing the different fault characteristics (relative magnitude, duration, failure mode). Even though its not enforceable, the informational note to Overcurrent reinforces, "the rules for overcurrent protection are specific for particular situations.". The handbook commentaries provide additional insight as well.


I'm assuming you deleted post #43 because you realized st, lt, or I couldn't be used to protect any and all three of those problems... For motor applications specifically, its not so much that its impractical, but 430.32(A)(1)/(B)(1), 430.42(D) and 430.51(C)(3) prohibit using only an instantaneous element.
you could have a motor built with higher temp insulation, bearings, cooling provisions, larger circuit equipment and use instantaneous, usually not practicle

Can you elaborate on instances where the NEC requires overcurrent protection but doesn’t require the devices to be listed? If one exists, then looking at the listing standards wouldn't help much.
I don't know of any, I didn't mean required ocpd, just things in general

I would maintain no not always. Also, LT can take a many seconds to trip for a short-circuit even though the pick-up setting is where the NEC requires... I doubt just because it will eventually trip you can get away with calling it short-circuit protection.
listing standard

If you use LT, ST or I elements to detect ground-faults on HRG or ungrounded systems, the breaker would fail to open, not because the protection device was oversized, but because LT, ST, and I are incorrect ways to detect that type of fault. Similarly, for instances where the maximum available short-circuit current is near or less than the load current (as is the case with long distribution lines and high impedance faults), you wouldn't say the protective device is oversized because it didn't trip.by oversized I mean the pickups are above the desired maximum ground fault level

None in particular.

Lets stick to NEC.

No it's only one random example.

Without getting into the definition of short-circuit (because the NEC is silent on that one) I think we can all agree a short-circuit is simply an unintentional connection. You don't actually need thousands of amperes to qualify it. Again, if a breaker fails to open in your example, it may have nothing to do with the protection device being oversized.
if its below required overload protection level then it's common sense ocpd wouldn't be required to trip for "short circuit protection", even the best relays can't pickup on all of what you are describing. and I point again to 250.4(a)(5) and (b)(4). I will check 11' if anything has changed


What about ground-faults in direct-buried cable, or faults conducted directly to earth? I'm not seeing the Effective Ground-Fault Current Path there.
correct and the typical requirement would be normal overload protection current level
2011
See in red above
 
My Incorrect Assumption

My Incorrect Assumption

No you didn't. Any peer group discussion I have been part of would consider the term "LSI" or "LSIG" to indicate an adjustable trip unit.
Fine. You win. I just learned that UL 489 defines LSIG parameters. I will try to avoid referring to characteristic curves this way unless I can find somewhere else that also uses these terms for equipment other than that covered by UL 489. Instead, I will refer to these parameters as: overload, locked-rotor, inrush, short-circuit, instantaneous, ground, inverse-time, definite-time curve(s)/region(s)/characteristic(s)/element(s) since most protective relaying references actually use those terms.

For all intents and purposes, please substitute the terms and consider the original post/question as still being valid. This subtle change shouldn't change much other than clear up some confusion regarding my choice of words.

The term T-M (in the context of molded case) would bring to mind the curve I posted earlier.
Yes, the thermal-magnetic curve you presented is the superposition of two elements; an overload curve/region and a definite-time (instantaneous) curve/region.
 