tonype
- New Jersey
The position is not so much a problem as being in the attic may.
Is this a readily accessible area?
There is a code section also about headroom and such. Gotta find it....lemme think ?
Ah, 110.26(3). Floor to ceiling height. Is this a dwelling unit? Exception may apply.
Assuming attic has finished floor, no?
Residential yes... at present no floor boards directly below.
readily accessible attic? Stairway or pull down ladder? Scuttle hole?
Hmmmm....
If one interprets the working space to require 6.5ft of headroom below the panel, then the install cannot be compliant with both 110.26(3) and 404.8(A), which puts a height limit of the same dimension on circuit breakers used as switches.
Hmmmm....
I think he is onto something,rember OP said this panel is ~30 degrees from vertical.Below the panel?
See existing resi exception. 110.26(3)
Below the panel?
Though I can see an issue with working clearances with a 4 ft tall cabinet in that situation, where a small 6 or 8 circuit loadcenter might not have the same issue.
You do need the head room but part of the headroom is bordered by the item you need clearance for.
30 degree angle would be little less than 6/12 pitch roof. If you had a 30 inch tall cabinet mounted at this angle the highest point is about 15 inches above the lowest point, the furthest rear point is about 26 inches further back then the furthest forward point.
correct, I screwed up there and gave measurements for 30 degrees from horizontal. You still have similar issues like I brought up, just not quite as severe as my examples.30* from vertical would be a 60* pitch, which is like 20/12 or so. 12/12 is a 45* pitch.
Still haven't looked into it but I still kind of have a feeling instructions or even general listing standards will require vertical mounting.