Re: Panel Rewire - Opinions, Please
Originally posted by jxofaltrds:
Question? Is this panel located on an exterior wall? The reason I ask is it looks like the entrance cable might be going through another unit.
The panel is on an exterior basement wall, the service cable goes out into the meter base located on the other side. This is a single family dwelling.
Originally posted by lady sparks lover:
1. Isn't there a 6 ft minimum clearance above panels??
2. I would separate the neutral bus, and equipment grounding bus conductors.
3. Check to see if the phases are balanced within 10% of each other.
1. I didn't set the panel, I just rewired the branch circuits, but yes, there is definitely a clearance issue with those steam pipes being there. Not sure how it passed inspection when it was installed (steam pipes were definitely there first).
2. That seems to be a common opinion, I think I'm gonna end up doing that.
3. I'll definitely take a look to see how balanced the legs are.
Originally posted by don_resqcapt19:
I believe that this panel has the bars permanently bonded and is listed "suitable only for use as service equipment". If the bonding is removable or installed in the field the listing would be "suitable for use as service equipment".
The bars aren't "permanently" bonded, not welded, anway. The bus bars are held onto the panel can by machine screws. One of the machine screws on each bus also threads through the bonding jumper before attaching to the panel can. The red sticker at the top of the can says:
"NOTICE: Non Service Equipment Applications Require Insulated Neutral Kit" So this panel could be used as a sub if an insulated neutral bus was installed in the field.
Originally posted by hurk27:
From what I can see, this is a main service panel and is only listed for use where it is required to be used as the main mean's of disconect but not as a sub panel.
I have noticed that Big John has referred to this panel as a sub panel and even said he was going to refeed it with 8/3 or 8/4
If it is a sub panel then the panel cannot be used.
John is there a main disconect outside for the service?
This is the main service panel. The 200A breaker at the top is the main disconnect, there is no other disconnect before it.
The sub panel I spoke of is in another part of the house, and is being fed from this panel.
The subpanel feeder I spoke of is visible in my first picture: The white cable that comes out of the right side of the service panel and goes into the junction box is that feeder. In the junction box, it splices into three #10 conductors that have been pulled through that piece of rigid you see entering the top of the j-box. It is those three #10s that I was talking about repulling with #8.
I hope that's a little clearer.
Originally posted by curt swartz:
After I looked at the picture more I now see the red sticker at the top which appears to say something about an insulated kit. I never used any Crouse-Hinds main breaker loadcenters but I guess they were primarily designed to service equipment installations which was probably what 99% of them were used for. If for some reason you wanted to use this load center for a non-service equipment installation you needed to purchase additional parts.
You're exactly right. As I said earlier, the sticker reads:
"NOTICE: Non Service Equipment Applications Require Insulated Neutral Kit" which you would have ot purchase if you wanted to use this panel as a subpanel.
Originally posted by awwt:
I can't remember: Was a permit pulled on this job?
Though I hate to admit it, I did not pull a permit, though I probably should have.
Thank you all for your input so far, I do appreciate it a lot.
-John