Panel Rewire - Opinions, Please

Status
Not open for further replies.

rickcham

Member
Re: Panel Rewire - Opinions, Please

Big John
Sorry my typing fingers do not always work in order, I did mean "GEC" I see it now thanks for the clarification on that :p
 
G

Guest

Guest
Re: Panel Rewire - Opinions, Please

Originally posted by charlie:
BTW (By The Way) IMHO (In My Humble Opinion) PETA means Pain In The - - -. :D <snip>
FYI: I think you mean PITA, not PETA. EOM. AFK.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Panel Rewire - Opinions, Please

Yes guys when I say PITA it means "Pain in the #%*". :(

As far as a meter can there is a strap between the lugs so even though the lugs are bolted to the can the strap will carry the majority of the current.

I will wait for more comments on this before I say more.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Panel Rewire - Opinions, Please

Originally posted by hillbilly:
Looking at the picture it appears that there is a aluminum bus between the two terminal bars. If there is, the install is OK in my opinion. If not, I don't believe any white wires should land on the left side (bonded) terminal.
I missed the aluminum buss, if it is there, then I agree with Hillbily, if there is no bus between these bars I stick with my original post.
 
G

Guest

Guest
Re: Panel Rewire - Opinions, Please

Personal preference here: I like to run my wires long inside the panel. I call it "longest possible path". When I land a wire in a panel I trim it so that it can reach the furthest breaker-- even if I will land the wire on the closest breaker. I keep my whites & bares fairly short-- but the hots go long. That way if I need to move a breaker up or down-- or ever go to a bigger panel I have some slack to make adjustments. Too long= good. Too short= bad. I don't like to stretch wires.

I notice a fair amount of wire stretching in this installation. I like to avoid that-- but I'm sure it was because of existing wiring.

I see a flat buss joining the right-hand neutral buss bar to the left-hand ground buss bar. I assume the neutral bar is bonded to the panel by a screw. For housekeeping, regardless of code I might have chosen to put the grounds on the left and the neutrals on the right.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: Panel Rewire - Opinions, Please

Big John

The work looks like a workmanlike job.

Question? Is this panel located on an exterior wall? The reason I ask is it looks like the entrance cable might be going through another unit.

Mike P.
 

tonyi

Senior Member
Re: Panel Rewire - Opinions, Please

Originally posted by awwt:
Personal preference here: I like to run my wires long inside the panel. I call it "longest possible path".
I originally did neat/short, but then started trying to do as you describe so any breaker can be moved to any slot later on for balancing purposes. I try to leave long neutral and gnds though as well. As breaker technology improves I expect we'll see more and more requiring the branch neutrals connected to breakers like GF/AF stuff. When everything has some slack, a subsequent panel swap becomes less of a spliced up mess and tapping into something like an AF/GF breaker where multiple wires might not be suppored becomes easier.

I fitted some GE arc faults in an apartment building a while back and it was about 30 year old GE panels with a neutral bar at the bottom. Where the branches came in to where the neutral bar lived, only about 2-3" and whoever hooked'em up originally cut that neutral wire close. I *just* had enough room to make the neutral splices to get to the AF's, but another 1/2" less and I'd have been into external j-boxes.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Re: Panel Rewire - Opinions, Please

Be careful, though a screw is included in the material list in 250.28(A) it is left out of 250.24(A)(4) unless there is a main bonding jumper in the form of a wire or bus-bar you cannot say these are electrically the same points. You cannot land the service neutral to a lug that is bonded to the enclosure unless there is a main bonding jumper in the form of a wire or bus-bare tying the grounding electrode conductor to the grounded conductor. Also keep in mind by definition the main bonding jumper must tie the equipment grounds to the grounded conductor. For these to be the same points there needs to be a main bonding jumper in the form of a wire or bus-bar sized according to 250.66
Perhaps I didn't explain myself correctly in my reply to Bob (iwire) but perhaps we're talking about the same thing only in a different way. In the breaker panels that I'm accustomed to using (Sq D) when you purchase a main breaker panel the neutral bar(s) float and they are internally strapped together. It's not until you install the green bonding screw that both buss bars become bonded to the enclosure. But, I can tell you from personal experience that the green bonding screw is not enough to clear a fault. So as an added bit of insurance, when I bring the #6 from the grounding electrode and the #4 from the cold water pipe into the panel I use a metal NMC connector, strip off the insulation from each wire where it passes through the connector, tighten down the connector and lock nut and then bond both wires to the buss bar. In doing this have I not met the conditions you've sited ?

In a main breaker panel there's no separation between neutrals and EGC's; electrically it's the same point via the buss bar. In a main lug panel there is a separation. Is it just me or is this a New Jersey thing ? (It's OK to say it if it's a NJ thing). ( It's OK to say if it's just me too but please explain why).

Now, I went back to look at Big John's panel. The neutral and EGC buss bars never floated (not even from the factory). They're bonded to the back of the cabinet right from the factory. Does this merely eliminate the need for the green bonding screw ? Should the panel be manufactured that way or was it field modified ?

Just curious,

Phil

PS : I know we're all just talking amongst ourselves here but I truly hope I haven't offended anyone with my comments.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Panel Rewire - Opinions, Please

Phil you certainly have not offended me, I am here to learn too.

Looking at the panel it must be listed as a main panel only with the neutral solidly bolted to the enclosure, I have not seen that before.

Bob
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Panel Rewire - Opinions, Please

Phil,
Does this merely eliminate the need for the green bonding screw? Should the panel be manufactured that way or was it field modified ?
I believe that this panel has the bars permanently bonded and is listed "suitable only for use as service equipment". If the bonding is removable or installed in the field the listing would be "suitable for use as service equipment".
Don
 

hurk27

Senior Member
Re: Panel Rewire - Opinions, Please

From what I can see, this is a main service panel and is only listed for use where it is required to be used as the main mean's of disconect but not as a sub panel.
I have noticed that Big John has referred to this panel as a sub panel and even said he was going to refeed it with 8/3 or 8/4

I'm probably gonna pull 8/4 or 8/3 and just put bond pushings on the conduit and use it as the EGC.
If it is a sub panel then the panel cannot be used.
John is there a main disconect outside for the service?
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: Panel Rewire - Opinions, Please

I was very confused about this panel from the picture at first. I have never seen a loadcenter that has the neutral factory bonded to the panel making it only rated for service equipment. After I looked at the picture more I now see the red sticker at the top which appears to say something about an insulated kit. I never used any Crouse-Hinds main breaker loadcenters but I guess they were primarily designed to service equipment installations which was probably what 99% of them were used for. If for some reason you wanted to use this load center for a non-service equipment installation you needed to purchase additional parts.
 
G

Guest

Guest
Re: Panel Rewire - Opinions, Please

I can't remember: Was a permit pulled on this job?
 

david

Senior Member
Location
Pennsylvania
Re: Panel Rewire - Opinions, Please

__________________________________________________
I'm probably gonna pull 8/4 or 8/3 and just put bond pushings on the conduit and use it as the EGC.
__________________________________________________

This statement was made in reference to the 10/3 going to the junction to the right of the panel.
 

big john

Senior Member
Location
Portland, ME
Re: Panel Rewire - Opinions, Please

Originally posted by jxofaltrds:
Question? Is this panel located on an exterior wall? The reason I ask is it looks like the entrance cable might be going through another unit.
The panel is on an exterior basement wall, the service cable goes out into the meter base located on the other side. This is a single family dwelling.

Originally posted by lady sparks lover:
1. Isn't there a 6 ft minimum clearance above panels??

2. I would separate the neutral bus, and equipment grounding bus conductors.

3. Check to see if the phases are balanced within 10% of each other.
1. I didn't set the panel, I just rewired the branch circuits, but yes, there is definitely a clearance issue with those steam pipes being there. Not sure how it passed inspection when it was installed (steam pipes were definitely there first).

2. That seems to be a common opinion, I think I'm gonna end up doing that.

3. I'll definitely take a look to see how balanced the legs are.

Originally posted by don_resqcapt19:
I believe that this panel has the bars permanently bonded and is listed "suitable only for use as service equipment". If the bonding is removable or installed in the field the listing would be "suitable for use as service equipment".
The bars aren't "permanently" bonded, not welded, anway. The bus bars are held onto the panel can by machine screws. One of the machine screws on each bus also threads through the bonding jumper before attaching to the panel can. The red sticker at the top of the can says: "NOTICE: Non Service Equipment Applications Require Insulated Neutral Kit" So this panel could be used as a sub if an insulated neutral bus was installed in the field.

Originally posted by hurk27:
From what I can see, this is a main service panel and is only listed for use where it is required to be used as the main mean's of disconect but not as a sub panel.
I have noticed that Big John has referred to this panel as a sub panel and even said he was going to refeed it with 8/3 or 8/4
If it is a sub panel then the panel cannot be used.
John is there a main disconect outside for the service?
This is the main service panel. The 200A breaker at the top is the main disconnect, there is no other disconnect before it.

The sub panel I spoke of is in another part of the house, and is being fed from this panel.

The subpanel feeder I spoke of is visible in my first picture: The white cable that comes out of the right side of the service panel and goes into the junction box is that feeder. In the junction box, it splices into three #10 conductors that have been pulled through that piece of rigid you see entering the top of the j-box. It is those three #10s that I was talking about repulling with #8.

I hope that's a little clearer.

Originally posted by curt swartz:
After I looked at the picture more I now see the red sticker at the top which appears to say something about an insulated kit. I never used any Crouse-Hinds main breaker loadcenters but I guess they were primarily designed to service equipment installations which was probably what 99% of them were used for. If for some reason you wanted to use this load center for a non-service equipment installation you needed to purchase additional parts.
You're exactly right. As I said earlier, the sticker reads: "NOTICE: Non Service Equipment Applications Require Insulated Neutral Kit" which you would have ot purchase if you wanted to use this panel as a subpanel.

Originally posted by awwt:
I can't remember: Was a permit pulled on this job?
Though I hate to admit it, I did not pull a permit, though I probably should have. :eek:

Thank you all for your input so far, I do appreciate it a lot.

-John

[ October 01, 2003, 01:26 AM: Message edited by: big john ]
 

rrrusty

Senior Member
Location
Colorado
Re: Panel Rewire - Opinions, Please

What I do is instead of running the NM into the side I take a 1x4 wood and secure it to the L/C and wall and run the NM thru the top of the L/C then I can take a piece of plywood and secure that to the 1x4 and have the cables safe from physical damage, and looks clean (still not to late to pull a permit)
 

rrrusty

Senior Member
Location
Colorado
Re: Panel Rewire - Opinions, Please

After reviewing the photo I noticed that not a lot of room for bringing the nm into the top; sorry:rolleyes:
 

david

Senior Member
Location
Pennsylvania
Re: Panel Rewire - Opinions, Please

I?m not going to discourage you from separating the neutrals from the equipment grounds, I hope you realize this to be a design preferance and not a code issue.
 

big john

Senior Member
Location
Portland, ME
Re: Panel Rewire - Opinions, Please

David,

I definitely understand that seperation of the EGCs and neutral conductors is a preference in this case.

The reason I started this thread was for feedback on what I might've been able to do to improve the quality of the installation. It sounds like seperating the EGs and neutrals would result in a cleaner-looking install, so at the least, it's something for me to think about.

-John
 