How do those breakers with two handles work? I don't recall ever seeing those. I'm referring to the ones with the blue paint. I see the tandems that are stacked but are the ones with two handles also tandems?Legal. That's the old tandem QO breakers.
Yes. There are terminals to attach wires to for each handle. This is how QO originally made tandems, like 700 years ago.How do those breakers with two handles work? I don't recall ever seeing those. I'm referring to the ones with the blue paint. I see the tandems that are stacked but are the ones with two handles also tandems?
For a while, Square D sold a "kit" that allowed you to tie the HANDLES of side-x-side tandems together to create a "quasi" quad, but they pulled it after a while, likely because of misuse. Handle ties do not qualify as "common trip", which is required if the load is 120/240V, such as a dryer or some air conditioners, where the main load is 240V by the blower motor is 120V. So that "quad" is possibly not legit.The two side-side tandem on the left hand side are not QO from Square D. Are they classified ones from another vendor?
There's no requirement to fix it, if it was legal at the time.So that "quad" is possibly not legit.
The handle ties on the 30s at the bottom look like the genuine QO kit I remember. The handle tie on the 20s bottom left looks ... custom.For a while, Square D sold a "kit" that allowed you to tie the HANDLES of side-x-side tandems together to create a "quasi" quad, but they pulled it after a while, likely because of misuse. Handle ties do not qualify as "common trip", which is required if the load is 120/240V, such as a dryer or some air conditioners, where the main load is 240V by the blower motor is 120V. So that "quad" is possibly not legit.
Not only that, many of them had push-in terminals instead of screw terminals. I couldn't find a pic showing the holes, but note in the first pic that there is no terminal screw hole:How do those breakers with two handles work? I don't recall ever seeing those. I'm referring to the ones with the blue paint. I see the tandems that are stacked but are the ones with two handles also tandems?
Push-in terminals were available but not common across the US.Not only that, many of them had push-in terminals instead of screw terminals. I couldn't find a pic showing the holes, but note in the first pic that there is no terminal screw hole:
QO panels have been made with allowances for tandem breakers since they were introduced in the late 50s, they used the QOxxyy numbering system.Nothing else fits the QO panel other than QO breakers unlike HOM that some can install other brand breakers but just not "legally", as nothing listed for Square D panel other than Square D breakers.
The breakers shown, the old "piggyback" or the other "side by side", both are examples of tandem breakers and were made by SD for their QO panels, and are allowed. The Piggybacks might be weak as they are quite old, and can be replaced by a "side by side" tandem. I don't think the old QO had any rejection device that limited the placement of the Tandem breakers, but it might not have been listed for tandem use. If the panel model is something like QO 20-40M it likely can have up to 20 tandems added.
Both Eaton and Siemens make Classified breakers for QO panels. Neither of those are available as quads though, or even tandems for that matter. Just 1 and 2 pole up to 50ANothing else fits the QO panel other than QO breakers unlike HOM that some can install other brand breakers but just not "legally", as nothing listed for Square D panel other than Square D breakers.
Interesting, Why would they make such as the "genuine" QO is, for the most part, readily available. Also how would the use of a "Classified" breaker in the SD panel, even though code allowed, effect the SD long standing policy that the use of any breaker other than "theirs" would void any panel warranty?Both Eaton and Siemens make Classified breakers for QO panels. Neither of those are available as quads though, or even tandems for that matter. Just 1 and 2 pole up to 50A
My favorite supply house is a Siemens and Eaton distributor. But they sell those classified breakers because they don't want their customers going somewhere else to get a QO breaker. In other words, money is why they exist.Interesting, Why would they make such as the "genuine" QO is, for the most part, readily available. Also how would the use of a "Classified" breaker in the SD panel, even though code allowed, effect the SD long standing policy that the use of any breaker other than "theirs" would void any panel warranty?
Jim, those look like Square D tandems to me. QO20303020 is a set of (1) 2030 and (1) 3020The two side-side tandem on the left hand side are not QO from Square D. Are they classified ones from another vendor?