Panelboard Questions

Jim, those look like Square D tandems to me. QO20303020 is a set of (1) 2030 and (1) 3020

The inner handle tie looks like a Square D but not sure about the outer handle tie.
I am talking about the two side by side single pole tandems on the upper left. I don't see any Square D logo or information stenciled on those breakers
 
Interesting, Why would they make such as the "genuine" QO is, for the most part, readily available. Also how would the use of a "Classified" breaker in the SD panel, even though code allowed, effect the SD long standing policy that the use of any breaker other than "theirs" would void any panel warranty?
If you were, for some reason**, to buy a Square D panel and buy ONLY the Siemens or Eaton Classified breakers, it would likely be a Code violation, because in the initial installation, those breakers would constitute a 110.3B violation of the PANEL listing, let alone the Square D panel warranty.

But AFTER a panel is installed and the warranty is already expired anyway, a contractor or homeowner doing retrofit work can ADD the Classified breakers.

**During the Covid supply chain crisis, this sort of thing was happening a lot more than it had before... One of my local Eaton distributors stocks the Eaton QO Classified breakers, which generally sat on the shelf collecting dust. But in 2021 they sold out completely.
 
I am talking about the two side by side single pole tandems on the upper left. I don't see any Square D logo or information stenciled on those breakers
Jim,
For some reason, the "newish" QOTs (side x side), have no logo on the front, brand new from the factory.

Z_-ur_fo5oz.JPG

Makes me wonder if maybe they are a little ashamed of themselves for being copycats...
 
Jim,
For some reason, the "newish" QOTs (side x side), have no logo on the front, brand new from the factory.

Z_-ur_fo5oz.JPG

Makes me wonder if maybe they are a little ashamed of themselves for being copycats...
They're probably made by an OEM who is neither of them, but sells it to both. I toured the Westinghouse plant in Beaver PA back in the last century and they were OEM'ing for Square D and Cutler Hammer, which was a separate company back then.
 
If you were, for some reason**, to buy a Square D panel and buy ONLY the Siemens or Eaton Classified breakers, it would likely be a Code violation, because in the initial installation, those breakers would constitute a 110.3B violation of the PANEL listing, let alone the Square D panel warranty.

But AFTER a panel is installed and the warranty is already expired anyway, a contractor or homeowner doing retrofit work can ADD the Classified breakers.

Since when does the code care whether a panelboard is still under warranty?
 
Interesting, Why would they make such as the "genuine" QO is, for the most part, readily available. Also how would the use of a "Classified" breaker in the SD panel, even though code allowed, effect the SD long standing policy that the use of any breaker other than "theirs" would void any panel warranty?
Why not get a proper QO breaker? Classified in my eyes should always be a last resort and if the proper manufactured breaker is available get it! In the mean time a classified may be a temporary solution but if the product that is right is available why would you settle for less? It’s your job to warranty and your license on the line!!! Ask a Ford dealership to install Chevy parts??? Ill warranty workmanship forever but a non listed product (not listed on the panels labels) would never be warrantied as at that point it should probably upgraded anyways. Vehicles didn’t used to have seatbelts but its a registration requirement now and as a licensed electrician you are responsible for it!!!
 
You could certainly operate each of those handles and verify the paint contamination is not giving any obvious trouble. Other than that the biggest problem that panel has from this view is bad labelling.
..
"Allowed" is funny wording. If it was legally installed originally nothing in the building code compels a proactive replacement. Much older panels are still happily working to this day. Just watch out for signs of failure. And watch for FPE or Federal Pacific breakers, which fail to trip in a way that won't be apparent on inspection.
By saying FPE i hope you ment FPE stablock because they were the ones that were known for trip failure and federal made multiple versions. Regardless i have seen panels/fused disconnects from the early 1900’s working, that doesn’t mean they are todays standards which is not only a safety concern but also old standards ruin electronics which are in everything, every day!!!!! If buss bars were sprayed with paint they are compromised, they make enough good connection to work but apply a heavy load to them and they fail! The panel boxes come with a cardboard cutout to put over it till you’re ready to put the cover on for a reason!!!
 
old standards ruin electronics which are in everything, every day!!!!!
Integrating electronics with overcurrent protection is a power-interruption nuisance, which ultimately fails in the energized state, violates UL 486, and has ruined this standard.
 
Last edited:
Interesting, Why would they make such as the "genuine" QO is, for the most part, readily available. Also how would the use of a "Classified" breaker in the SD panel, even though code allowed, effect the SD long standing policy that the use of any breaker other than "theirs" would void any panel warranty?
I once seen some QO classified breakers at local lumberyard. This been at least 20 years ago and I don't remember who actually manufactured them. They were more expensive to purchase than genuine QO breakers were at that time.
 
They're probably made by an OEM who is neither of them, but sells it to both. I toured the Westinghouse plant in Beaver PA back in the last century and they were OEM'ing for Square D and Cutler Hammer, which was a separate company back then.
Was this company making components or finished products.

I been to plant in Lincoln NE that assembled mostly QO breakers back in I believe 1988. I would guess majority of components came from elsewhere and maybe even from places that made components for other names of finished products.

AFAIK Schneider still has this plant but the QO assembly operation has moved to Mexico, not sure what they are doing in Lincoln plant.
 
My guess is the number of circuits is a heat rise issue.
Notice how the asterisk limits the non-CTL breakers to 20A max.
 
Handle ties do not qualify as "common trip", which is required if the load is 120/240V, such as a dryer or some air conditioners, where the main load is 240V by the blower motor is 120V.
An individual (supplying only one piece of utilization equipment, like a dryer or a stove) MWBC does not require common trip, so a handle tie on two single pole breakers would suffice. See 210.4(C) Exception 1.

Cheers, Wayne
 
AFAIK Schneider still has this plant but the QO assembly operation has moved to Mexico, not sure what they are doing in Lincoln plant.
As far back as the early 80s, QO breakers were made in Ireland and Mexico as well as the Lincoln plant.
 
An individual (supplying only one piece of utilization equipment, like a dryer or a stove) MWBC does not require common trip, so a handle tie on two single pole breakers would suffice. See 210.4(C) Exception 1.

Cheers, Wayne
Unless something has changed from the 2017, that's not what 210.4(C) ex 1 says. It's saying the load does not have to be line to neutral only if its one piece of utilization equip. Doesn't mention type of OCPD.

240.15(B)(1) says handle ties for a MWBC can only be used for line to neutral loads, so a stove, or dryer would require a 2-pole breaker.
 
Unless something has changed from the 2017, that's not what 210.4(C) ex 1 says. It's saying the load does not have to be line to neutral only if its one piece of utilization equip. Doesn't mention type of OCPD.
Right, but as 210.4(C)'s base text prohibits powering an L-L load from an MWBC, you have to comply with one of the exceptions in order to do so. Exception 1 allows it if the MWBC supplies only one piece of equipment. Exception 2 allows it if the OCPD is common trip. So in that sense exception 1 is an alternative to providing common trip, which Jraef incorrectly stated was always required.

Note that 240.15(B) also bears on this question, but 210.4(C) is more restrictive.

Cheers, Wayne
 
Right, but as 210.4(C)'s base text prohibits powering an L-L load from an MWBC, you have to comply with one of the exceptions in order to do so. Exception 1 allows it if the MWBC supplies only one piece of equipment. Exception 2 allows it if the OCPD is common trip. So in that sense exception 1 is an alternative to providing common trip, which Jraef incorrectly stated was always required.

Note that 240.15(B) also bears on this question, but 210.4(C) is more restrictive.

Cheers, Wayne
That is not correct. Ex 2 says this
Exception No. 2: Where all ungrounded conductors of the multiwire
branch circuit are opened simultaneously by the branch-circuit overcurrent
device.
That's says the OCPD has to open the circuit simultaneously. Handle ties wouldn't always open both poles on a tripped condition.

Think about it. If handle ties were used on a MWBC for a 240/120V piece of equipment and the 120V portion tripped, that would leave one breaker energized. This would be a hazard to anyone working on the equipment.
 
That is not correct. Ex 2 says this

That's says the OCPD has to open the circuit simultaneously. Handle ties wouldn't always open both poles on a tripped condition.
Correct, if your MWBC is supplied by a common trip OCPD, then exception 2 applies. That would let one MWBC supply multiple 240V or 120V/240V pieces of equipment.

But if your MWBC supplies only one piece of equipment, exception 1 applies, and there is no requirement for common trip. You can use two single pole breakers with a handle tie to supply a 120V/240V range, say, as long as nothing else is supplied by that MWBC.

If I've overlooked a different code section that would prohibit that installation, please let me know, but it complies with 210.4(C) and 240.15(B).

Think about it. If handle ties were used on a MWBC for a 240/120V piece of equipment and the 120V portion tripped, that would leave one breaker energized. This would be a hazard to anyone working on the equipment.
Not following--anyone working on the equipment is expected to turn off the breaker, and the handle-tie will ensure that both legs are turned off.

Cheers, Wayne
 