Would a panel be considered an outlet. Would it have to be all on arcfault. Even the feeder!
Roger, I agree with you that the AFCI protection of the feeder to a panel in a bedroom location falls outside of the limits of 210.12, with the unusual exception of a panel on a 15 or 20 Amp 125 Volt feeder.
However, given the Definitions of:
- Premesis Wiring (System)
- Controller
- Outlet
A circuit breaker (used as a Controller) has an Outlet present in it because the wiring internal to controllers is not part of the Premesis Wiring (System).
I conclude that a panel is a multioutlet assembly, some of which are 15 or 20 Amp 125 Volt, and therefore fall under 210.12(B) when the panel is inside the "living spaces" listed in 2008 NEC 210.12(B), or inside the bedroom for those jurisdictions enforcing the 2005 NEC.