250.122(A) second paragraph says "Equipment grounding conductors shall be permitted to be sectioned within a multiconductor cable, provided the
combined circular mil area complies with Table 250.122."
Plus, there's 310.10(G)(5) on sectioned EGCs. Also, there's the general argument that since 310.10(G)(1) only restricts parallel installations for non-EGCs, that means EGCs can be paralleled in any size. Likewise, while 310.10(G)(5) explicitly permits sectioned EGCs in cables, it doesn't prohibit them in other cases.