Parallel Cables grounding

Status
Not open for further replies.

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I can't put my finger on it in the Code but I thought it addressed multiconductor cables with multiple EGCs allowing the area of multiple smaller conductors to be combined. His cables have 3-#2 EGC which would have a combined area greater than the required 3/0.
Am I mistaken ??
I just read 250.122 and I didn’t see that is allowed, so in a word, yes
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I reviewed 250.122. One part for cables in a raceway states the cable individual EGC are connected together, and the correct size equipment grounding conductor is also installed, and connected to the individual connectors.
 

mooreaaryan

Member
Location
Bakersfield CA
Occupation
Electrician
Dont know. What is the distance? What is the load? Is there a VFD? If so, what is the nameplate on the VFD? Maybe the designer/engineer forgot to change from 2-3/C #500 to just a 3/C #500 and it was an oversight.
This is very likely…100 up drive. Our previous “copy and paste” project was 150hp
 

mooreaaryan

Member
Location
Bakersfield CA
Occupation
Electrician
A 3 grounded cable is usually for a VFD. Probably 3 #6 as that is the most common. Terminate the three grounds in an Ilsco multi lug. 3 #6 in 1 #2 out. as mentioned, twisting together is a code violation.
10-4. Thank you I appreciate the input sir. We will be correcting Monday
 

mooreaaryan

Member
Location
Bakersfield CA
Occupation
Electrician
Everyone. Thank you for helping out… turns out that myself, my bosses and our pm have been do it wrong for 10,24,26 years respectfully. Just goes to show just because you do it one way doesn’t mean your right Always be willing to take lessons regardless of the cost! Have a good one stay safe
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I just read 250.122 and I didn’t see that is allowed, so in a word, yes
250.122(A) second paragraph says "Equipment grounding conductors shall be permitted to be sectioned within a multiconductor cable, provided the
combined circular mil area complies with Table 250.122."

Plus, there's 310.10(G)(5) on sectioned EGCs. Also, there's the general argument that since 310.10(G)(1) only restricts parallel installations for non-EGCs, that means EGCs can be paralleled in any size. Likewise, while 310.10(G)(5) explicitly permits sectioned EGCs in cables, it doesn't prohibit them in other cases.

Cheers, Wayne
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Wow. I have been completely ignorant to this Thank you so much for clarifying this. I appreciate it .
You are not the first person to have the wrong size EGC.
Everyone. Thank you for helping out… turns out that myself, my bosses and our pm have been do it wrong for 10,24,26 years respectfully. Just goes to show just because you do it one way doesn’t mean your right Always be willing to take lessons regardless of the cost! Have a good one stay safe
You are welcome. Thanks for your asking and using the forum.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
250.122(A) second paragraph says "Equipment grounding conductors shall be permitted to be sectioned within a multiconductor cable, provided the
combined circular mil area complies with Table 250.122."

Plus, there's 310.10(G)(5) on sectioned EGCs. Also, there's the general argument that since 310.10(G)(1) only restricts parallel installations for non-EGCs, that means EGCs can be paralleled in any size. Likewise, while 310.10(G)(5) explicitly permits sectioned EGCs in cables, it doesn't prohibit them in other cases.
So, I was correct 'way back in post #15?
 