If I have to parallel my conductors to be sized at 800 kcm(490 amps). If I want to parallel them I could use 2- 250(255*2=510amps)
Now suppose by equipment grounding conductor in a different example needs to be 500 kcm based on 250.122. Do I use Table 8 and use 2-250 kcm or do I use table 310.15(B)(16) as done above for the ungrounded conductors assuming a 75C rating. Thus 500 kcm(380 amps) so I could use 2- 3/0 (200 *2=400 amps).
I feel I should know this. In this example I want to parallel the equipment grounding conductor in one conduit
Now suppose by equipment grounding conductor in a different example needs to be 500 kcm based on 250.122. Do I use Table 8 and use 2-250 kcm or do I use table 310.15(B)(16) as done above for the ungrounded conductors assuming a 75C rating. Thus 500 kcm(380 amps) so I could use 2- 3/0 (200 *2=400 amps).
I feel I should know this. In this example I want to parallel the equipment grounding conductor in one conduit