(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded
circuit shall be permitted to be connected in parallel (electrically
joined at both ends) only in sizes 1/0 AWG and larger
where installed in accordance with 310.10(H)(2) through
(H)(6).
Exception No. 1: Conductors in sizes smaller than 1/0 AWG shall be
permitted to be run in parallel to supply control power to indicating
instruments, contactors, relays, solenoids, and similar control devices,
or for frequencies of 360 Hz and higher, provided all of the following
apply:
(a) They are contained within the same raceway or cable.
(b) The ampacity of each individual conductor is sufficient to
carry the entire load current shared by the parallel conductors.
(c) The overcurrent protection is such that the ampacity of each
individual conductor will not be exceeded if one or more of the parallel
conductors become inadvertently disconnected.
Exception No. 2: Under engineering supervision, 2 AWG and 1 AWG
grounded neutral conductors shall be permitted to be installed in parallel
for existing installations.
Informational Note to Exception No. 2: Exception No. 2 can be
used to alleviate overheating of neutral conductors in existing
installations due to high content of triplen harmonic currents.
(2) Conductor and Installation Characteristics. The paralleled
conductors in each phase, polarity, neutral, grounded circuit
conductor, equipment grounding conductor, or equipment
bonding jumper shall comply with all of the following:
(1) Be the same length.
(2) Consist of the same conductor material.
(3) Be the same size in circular mil area.
(4) Have the same insulation type.
(5) Be terminated in the same manner.
(3) Separate Cables or Raceways. Where run in separate
cables or raceways, the cables or raceways with conductors shall
have the same number of conductors and shall have the same
electrical characteristics. Conductors of one phase, polarity,
neutral, grounded circuit conductor, or equipment grounding
conductor shall not be required to have the same physical characteristics
as those of another phase, polarity, neutral, grounded
circuit conductor, or equipment grounding conductor.
(4) Ampacity Adjustment. Conductors installed in parallel
shall comply with the provisions of 310.15(B)(3)(a).
(5) Equipment Grounding Conductors. Where parallel equipment
grounding conductors are used, they shall be sized in
accordance with 250.122. Sectioned equipment grounding
conductors smaller than 1/0 AWG shall be permitted in multiconductor
cables, if the combined circular mil area of the
sectioned equipment grounding conductors in each cable
complies with 250.122.
(6) Bonding Jumpers. Where parallel equipment bonding
jumpers or supply-side bonding jumpers are installed in raceways,
they shall be sized and installed in accordance with
250.102.