Gary, look at the General Rule of 310.10(H):
I don't see Equipment Grounding Conductors included in the list of conductors in this rule that establishes the 1/0 and larger limit.
Hello!
Yes, Im not surprised. And I never thought someone would try to parallel an ECG in the same conduit. But, that is what the thread was based on. It's a good idea for large wires that are hard to purchase.
I said I was the inspector. I am the AHJ. Since this is a bastard installation and not anything I have ever seen in the codebook,
I would not pass two #XX less than 1/0 in the same conduit to make the right size single wire that is approved by the code, which is under 310.10(H) for parallel conductors for load. If they tried this under a bigger breaker, which would require a bigger wire, and they paralleled those large wires and larger than #1, I would approve it.
I have no idea why they limit parallel on conductors to 1/0 and larger, but I see no reason now to allow two smaller in parallel now to trip a breaker when they wont allow it for the load. Under fault, it is a load.
If you have two conduits with feeders in parallel, it only takes one conduit with proper ECG fault to trip the breaker. But it takes two conduits in parallel to get the ampacity you want. There is a difference here when it comes to parallel, IMO
Guys, this is just an opinion.
It's nice being the AHJ.