Think about Augie47's quote from Soares . . . the EGC has to be full sized because if there is a line to EGC fault in a run of parallel energized conductors the fault current into the EGC will come from both directions (from both ends) along the energized conductor. If you have only one of two conduits with a proper EGC, how do you know before hand that that is the conduit that will have the line to EGC fault?
But the fault can go "both ways" on the EGC too, so seems like, at least for two sets in parallel, a half size EGC in each pipe would be sufficient.