I have searched this forum for a clear answer. I believe the inspector to be mistaken by NEC 300.20. and 300.20 (b)
We have (3) 4" chase nipples installed from a ferrous gutterway attached to a feeder section. Each set of phases is being ran through each chase. Example, 3- A phase conductors, 3- B phase conductors, and 3- C phase conductors through each chase nipple into the enclosure. There is no grounded conductor.
According to my understanding, this would violate 300.20 and cause induction due to the ferrous metal enclosure. The inspector seems think that it is not a violation since its only a chase nipple and its a short distance. I would love some clarification.
Everything I have seen through my search indicates nipples (which I understand these are) and PVC conduit. There is no clear cut answer.
Thanks for your help
We have (3) 4" chase nipples installed from a ferrous gutterway attached to a feeder section. Each set of phases is being ran through each chase. Example, 3- A phase conductors, 3- B phase conductors, and 3- C phase conductors through each chase nipple into the enclosure. There is no grounded conductor.
According to my understanding, this would violate 300.20 and cause induction due to the ferrous metal enclosure. The inspector seems think that it is not a violation since its only a chase nipple and its a short distance. I would love some clarification.
Everything I have seen through my search indicates nipples (which I understand these are) and PVC conduit. There is no clear cut answer.
Thanks for your help