Square D does that thing where they run parallel conductors from the meter to the main disco.
I want to go into the ATS with single 3/0 conductors, and transition to the parallel conductors in the meter/main, (plenty of room) with a Polaris connector.
I don’t know of anything that would prohibit that. I’m not familiar with any provision that requires parallel conductors to remain parallel to any specific point.
Square D does that thing where they run parallel conductors from the meter to the main disco.
I want to go into the ATS with single 3/0 conductors, and transition to the parallel conductors in the meter/main, (plenty of room) with a Polaris connector.
I don’t know of anything that would prohibit that. I’m not familiar with any provision that requires parallel conductors to remain parallel to any specific point.