powerplay
- In front of a computer.
Have you tried 4 sets of smaller wire? It may be harder to terminate - you may even need a terminal box at each end to get the wire back to something that will land on the breaker.
But with really large wire (750KCM) the current tends to flow on the outside of the cable, and not in the middle. That means you have a lot of extra copper that isn't helping much.
For example, I think 4 sets of 3/0 is less copper, but only about 70% of the voltage drop.
Thanks for the insight...
I thought the individual strands that make up the larger size wires had the current travelling on the outside, rather than the current travelling along the outer strands of the one insulated phase wire?