Got it, With all due respect unless there is a real OCPD (a fused disconnect) at each pole, I see 240.10 as classifying the entire thing a 40 Amp outside branch circuit. I looked in 225 for exemptions and 225.7 just re-invokes 210.
We are allowed to tap 'fixture wires' per 240.21
That sends us to → 210.20(B) Flexible cords and fixture wires shall be
protected in accordance with 240.5.
240.5 has two options:
→ 240.5 Protection of Flexible Cords, Flexible Cables, and
Fixture Wires. Flexible cord and flexible cable, including tinsel
cord and extension cords, and fixture wires shall be protected
against overcurrent by either 240.5(A) or (B).
→ 240.5 (A) with your supplemental fuse a smaller than 12AWG conductor can be used as fixture wire.
OR (without the fuse)
→ 240.5(B)(2)(5) → 40A circuit requires 12AWG fixture wire.
However in all this I see no modification of the rules requiring a heavy duty lampholder.
However, after looking up that spec sheet for your fixed lighting units it appears they
do not contain a lampholder, which if true makes them 'other utilization equipment', and so the whole lampholder issue is moot.
I think in both scenarios the 40A circuit is a branch circuit and 210.23(C) applies to both. A 15 or 20A branch circuit would need to be created by a real OCPD not a supplemental one. I would be interested to see those specs on the fuse holder.
Tap rule:
240.21 Location in Circuit. Overcurrent protection shall be
provided in each ungrounded circuit conductor and shall be
located at the point where the conductors receive their supply
except as specified in 240.21(A) through (H). Conductors sup-
plied under the provisions of 240.21(A) through (H) shall not
supply another conductor except through an overcurrent protec-
tive device meeting the requirements of 240.4.
(A) Branch-Circuit Conductors. Branch-circuit tap conduc-
tors meeting the requirements specified in 210.19 shall be permit-
ted to have overcurrent protection as specified in 210.20.
→ 210.20 (B) Conductor Protection. Conductors shall be protected in
accordance with 240.4. Flexible cords and fixture wires shall be
And as long as we don't have the lampholder I say the branch circuit technicalities give us the green light.
And if not there is always 90.4
Happy New Year!