Good point, is this box connected to conduit or NM? If conduit I would bond fixture to the box,if there is a EGC I would attach bonding pigtail to box, EGC to pigtail, bond wire from fixture to pigtail, if NM I would wrap EGC around ground screw and then to fixture or install bond pigtail in box and attach all EGC'siwire said:fbhwt
Let me ask you something.
When you install a surface mounted ceiling fixture on a metal box do you,
Ground the box and the the light fixture?
or
Do you just ground the light fixture and rely on just the fixture mounting screws to ground the box?
Now which are people more likely to come into contact with, a recessed metal ceiling box or a site pole?
------------------------------------------------------------------------------
Do it right and connect the EGC directly to the lighting pole at the ground lug in the hand hole as required and continue it to the light fixtures green wire.
By the way 250.148(B) requires that the grounding be maintained even with the removal of a device or luminaire and 250.148.(C) requires it done with a means that serves no other purpose.
I should have been more explicit as far as the pole, EGC to GEC pigtail,EGC to green wire at fixture