Re: pedestal combination meter and main
Yes, I have opened a large number of pedestals, and no I haven't seen any of the bonds that you are talking about. I am only one guy, I have only been doing this for 15 years, and I don't claim to have seen every installation. I still don't think the bonding takes place here in Colorado between residential power pedestals and phone or coax pedestals.
Thanks for pointing out the code section in the NESC, I have been poking around in it for some time in order to increase my own knowledge. This is a curiosity thing as I agree with you that I don't
need the knowledge. I still seek it, however.
My statement earlier -
If that is the case, there are millions of overhead three wire residential drops in Colorado alone that need to be changed...
did not mention services, although I probably overstated the millions section (likely more in the hundreds of thousands). I also did not add the term underground to go with overhead in my haste. Let me restate it...
If that is the case, there are hundreds of thousands of residential overhead feeders (drops if you will) and underground feeders (laterals if you will) that only have three conductors in them. All of these would need to be changed in order to meet your interpretaion of the feeder requirement as I agree that all phone and coax systems are bonded to the electric utility at some point in their system.
In short, my disagreement is not in the above aspects of this discussion. It is that a four wire feeder is not required by the NEC in the original scenario.
250.32(B)(2) clearly states...
"there are no continuous metallic paths bonded to the grounding system in both building or structures involved..."
This to me means that the continuous metal paths would need to be directly between the power pedestal at the edge of the property and the home that it feeds. The continuous metal paths that you are referring to may take place at the phone site that may be a mile away. I think the installation as I have described is safe, and within the intentions and wording of the NEC. This is why it is included as an option in the code.
For clarification -
If the power pedestal and the phone/coax pedestal are in fact bonded directly to each other, than a four wire feeder would be required. This was a good point to make, as I have never seen it, the way I do things in Colorado may not work for people in different parts of the country. The part about never using a three wire feeder I still have to respectfully disagree with.
Enjoy your day!