Re: pedestal combination meter and main

Ok I agree with that but what about when you use 230.40 Exception 3?

If this is used then you would still have service entrance conductors and if you ran these to the garage then with what your saying it would not matter if there is also other parallel paths? :confused:

[ February 08, 2005, 05:57 PM: Message edited by: hurk27 ]
 
Re: pedestal combination meter and main

Wayne, that is correct. Consider that you are still on the line side of the service disconnecting means and overcurrent protection. Grounding is done differently. The islands do not form until after the service disconnecting means and overcurrent protection. :D
 