Right if it's something where a few drips of water won't matter. For example the nipple between a CT cabinet and the meter socket. No I'm not going to use a Myers hub on the side of the CT can for the 1" nipple. A 3R tap box below a meter is another one. I'll probably just use a rigid nipple and a ceiling lock nut, I don't see the need for a Meyers hub. I'm always going to arrange the splices such that they can't be dripped on and water won't surface tension down the conductor to the splice. EMT rain right couplings are another. There are already code sections that deal with water in conduits such as raceways shall be allowed to drain and conductors rated for wet locations. So I am using the rain tight fittings to pass my inspection, and I'm not concerned about some water in the conduit. So I'm going to make a call on what to use based on the importance of keeping water out. Yes of course there are situations I would definitely use a Myers hub.
I don't think I said that. I just said hubs were not listed for anything other than RGS.
I think I pretty much responded to this.
Correct, many times it does not matter.
. Right. So assume water will get in, allow for drainage with weep holes and such and arrange splices to be clear of drips and such, and use what fittings you need to pass your inspection.
JAP>