Penetrating the top of a outdoor NEMA 3R Gutter/Through?

Status
Not open for further replies.

Sberry

Senior Member
Location
Brethren, MI
Occupation
farmer electrician
After I did this thought of a bit cheaper way. Twas a long time ago, before this stuff and convenient shopping. But would have went out the back with 1 and LB out the side with the other one instead of this raceway. service 400.JPG
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
With the integral O ring on a Meyers hub I wouldn't be relying on it too much for bonding either.

Jap
Right, but you are required to bond the raceway. If both ends have that stupid gasket - sooner or later the raceway isn't bonded very well even if you pulled a green inside.
 
  • Like
Reactions: jap

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Power Company's overhead drops most generally attach to Service Masts.
Most Service Masts are required to be Rigid conduit.
Rigid conduit is compatible with most hubs unlike EMT Compression or RT connectors.

Thus our dilemma.

JAP>
If the "Mast" is supporting the service drop yes. If the drop is anchored to the building many will just run EMT for the raceway going up to the drop.
 

farmantenna

Senior Member
Location
mass
Inspector tried to reject this UL approved product. "It's approved. Do you have you're own listing lab in your basement?"
 

Attachments

  • e943jw.pdf
    44.5 KB · Views: 28

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Inspector tried to reject this UL approved product. "It's approved. Do you have you're own listing lab in your basement?"
The inspection authority has to approve everything per 110.2 and there is no requirement that the inspection authority approve listed products. They should, but they are not required to do so.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
These sealing washers work well and spec sheet calls out using for sealing fittings to enclosures.
Last time I looked at instructions for sealing washers, they said to put the washer on the outside of the enclosure against the fitting.
 