rszimm
Member
- Location
- Tucson, AZ
Brand new 3HP Pentair pool pump, computer controlled, variable speed. Connected via 2 pole GFCI breaker (no load neutral to the pump). Nuisance trips about once per day. The pool company tells me this is so common that they generally swap out the GFCI breaker as soon as the inspection is complete with a standard 2 pole breaker. They give me some gobbledygook about inductive loads, blah blah. Being a EE and knowing that GFCIs are pretty simple (just run all the load wires through a coil and measure the current coming off that to make sure all the current going out one line comes back on one of the others), this just doesn't sit well with me. Inductive loads or no; computer controlled or no, if current is on one line and not coming back on another, it's by definition going through either the grounding conductor or into the actual physical ground. I suppose some high speed switching of the motor from the variable speed controller could theoretically induce a small amount of current in the case or the grounding conductor, but that would seem to be a design fault in the pump.
Anyone else run into this?
Anyone else run into this?