wptski
Senior Member
- Location
- Warren, MI
Your extension cord test in Post #5 describes an open ground wire, doesn't it? The Ideal 61-501 shows an open ground. Using a high impedance meter this will show up as stray voltage.Details please?
In your field problem, it "appears" that all wires are properly connected. Three wire conductor is used because half of the duplex is switched, your picking up stray voltage from the extra wire.
A Fluke VoltAlert 1AC-A-II will also detect that stray voltage on a open ground too. It wil react the same way on a open neutral also. Stray voltage isn't always a bad thing in some ways.