This topic started in another thread on a different topic (linked here). But I want to explore this issue in more detail, so I'm starting a new thread.
Background:
There are two large pumps in a remote pump house; the pumps are used for discharging rainwater and ground water off a large property that is below sea level. The pumps are driven by electric motors, one old (no nameplate data) and one fairly new (~3-4 years old). They both operate on 3-Phase 240VAC power and both have separate soft-starters. The new pump draws 100A and the old pump draws 60A. When measuring the current draw on each of the three phases, I'm seeing 12-15% consistently greater current on one leg (always the same leg, for both pumps). This occurs both when running the pumps individually or both simultaneously. Our electrical service is 3-phase delta with 208 stinger leg. In addition to the pumps, there are also have some small 120V loads on this service:
History:
Originally, the pump house only had 100A service. When the new pump was installed, the 100A main breaker would always trip after the new pump would run for a short time, so it was taken offline. Obviously, the service was undersized. But in addition, the POCO had investigated and said there was a voltage imbalance and that they would be replacing the transformer. (This was before I was involved in the project, so I don't have more specifics.)
I upgraded the service entrance to 200A, upgraded the feeders and branch conductors to the motors, etc. POCO came and cut-over the drops from the pole, still using the existing transformers. When running the new pump, the current draw on all three legs would slowly rise until the over-current protection in the soft-starter would shut it down. This is where I start taking lots of voltage and current measurements and identified the imbalance in amps on the one leg. POCO came out and put a logging meter on our service, but suggested the problem was with our equipment. This analysis didn't make sense to me because the imbalance is present on both pump motors, on the same leg every time, and proportionally equal (always 12-15% higher on that one leg). Sometime later, the transformers servicing the pump house took a lighting hit during a storm. While waiting for POCO to replace the transformers (which they did, with larger transformers, pictured below), we rented a commercial diesel generator to power the pumps. While operating on the diesel generator, there was NO current imbalance on the phases, however the new pump was still experiencing the problem of increasing current draw on all three legs. I discovered that the shaft on the new pump was binding and causing the overload condition. We pulled the pump and sent it back to the manufacturer for repair. Pump is now back and re-installed. It now turns freely and it no longer has any problems with increasing current draw. However, I am still able to measure the same current imbalance.
I suspected that the imbalance problem had to do with the quality of the power from the POCO. But Augie and Hv&Lv pointed out that the problems are more likely due to the inherent nature of deriving 3-phase power using 2-transformers in a delta configuration. Since I can't import those two informative posts I received in the other thread, I'll quote them here:
Admittedly, the theory and implementation of supplying 3-phase power is going way past my area of expertise. But it would appear that we need to get the POCO to bring a third phase and install three transformers. Does the POCO have an obligation to do this? It seems that with a 15% phase imbalance, we are shortening the lives of our motors considerably. Also, if the POCO does upgrade us to "true" 3-phase service, will we still be able to run our 120V panel off one of the 3 hot legs?
Any input on this problem would be greatly appreciated.
Background:
There are two large pumps in a remote pump house; the pumps are used for discharging rainwater and ground water off a large property that is below sea level. The pumps are driven by electric motors, one old (no nameplate data) and one fairly new (~3-4 years old). They both operate on 3-Phase 240VAC power and both have separate soft-starters. The new pump draws 100A and the old pump draws 60A. When measuring the current draw on each of the three phases, I'm seeing 12-15% consistently greater current on one leg (always the same leg, for both pumps). This occurs both when running the pumps individually or both simultaneously. Our electrical service is 3-phase delta with 208 stinger leg. In addition to the pumps, there are also have some small 120V loads on this service:
- The electronic pump controller (for starting and stopping the pumps based on water level in the collecting pond).
- The anti-condensation heating coils in the new pump motor (low current; disconnected when the pump is operating).
- Two branch circuits for dusk-to-dawn exterior lighting (less than 10A each).
- Interior lights for the pump house (normally not in use).
- General purpose outlets in the pump house (normally not in use).
History:
Originally, the pump house only had 100A service. When the new pump was installed, the 100A main breaker would always trip after the new pump would run for a short time, so it was taken offline. Obviously, the service was undersized. But in addition, the POCO had investigated and said there was a voltage imbalance and that they would be replacing the transformer. (This was before I was involved in the project, so I don't have more specifics.)
I upgraded the service entrance to 200A, upgraded the feeders and branch conductors to the motors, etc. POCO came and cut-over the drops from the pole, still using the existing transformers. When running the new pump, the current draw on all three legs would slowly rise until the over-current protection in the soft-starter would shut it down. This is where I start taking lots of voltage and current measurements and identified the imbalance in amps on the one leg. POCO came out and put a logging meter on our service, but suggested the problem was with our equipment. This analysis didn't make sense to me because the imbalance is present on both pump motors, on the same leg every time, and proportionally equal (always 12-15% higher on that one leg). Sometime later, the transformers servicing the pump house took a lighting hit during a storm. While waiting for POCO to replace the transformers (which they did, with larger transformers, pictured below), we rented a commercial diesel generator to power the pumps. While operating on the diesel generator, there was NO current imbalance on the phases, however the new pump was still experiencing the problem of increasing current draw on all three legs. I discovered that the shaft on the new pump was binding and causing the overload condition. We pulled the pump and sent it back to the manufacturer for repair. Pump is now back and re-installed. It now turns freely and it no longer has any problems with increasing current draw. However, I am still able to measure the same current imbalance.
I suspected that the imbalance problem had to do with the quality of the power from the POCO. But Augie and Hv&Lv pointed out that the problems are more likely due to the inherent nature of deriving 3-phase power using 2-transformers in a delta configuration. Since I can't import those two informative posts I received in the other thread, I'll quote them here:
Some of the far more learned than I can explain what I am referencing, but over the years I have encountered several pump situations which have 2 pot 240/120 delta 3 phase supplies which for reasons beyond my comprehension reek havoc with pumps, especial submersible pumps. We had a water-crest farm in our area that had 20 or 30 pumps that were constantly going out. The brainiacs from TVA were called in and concluded that due to the nature of the loads, only a "true" 3 phase system with 3 phase primary and 3 pots would alleviate the problem. At much expense POCO changed the system and the problems disappeared. The engineers had a great explaination which was way over my head,
Don't know who the POCO reps were, but they may very well have been lineman. Most lineman fail to realize that an open delta is only good for 87% of transformer bank rating. Normally the larger pot is used for lighting loads (120/240) So if you had a 10 kVa and a 15kVa XF, the kva rating for the bank would be about 22 kVa. Once you start loading these banks down, as many engineers like to do to control line loss, you start to have voltage imbalances that cause the motors to heat up excessively, thus shortening their life. Another thing that adds to the voltage imbalance is improperly matched impedances in transformer banks. this just adds to the voltage imbalances. Aren't motors rated for about 1% voltage imbalance anyway? A 2 pot bank is generally saved for light 3 phase loads along with single phase loads. A lot of POCO's will try to stretch out these banks with v phase feeding them. Your motors are cheaper than the POCO's third phase and the additional XF, especially if the nearest third phase is 3 or 4 miles down the road. When we have a high leg pot go out on a large load, I like to upsize the XF based on the demand reading on the meter. A larger XF is also cheaper than a third phase if the load isn't too large.
Admittedly, the theory and implementation of supplying 3-phase power is going way past my area of expertise. But it would appear that we need to get the POCO to bring a third phase and install three transformers. Does the POCO have an obligation to do this? It seems that with a 15% phase imbalance, we are shortening the lives of our motors considerably. Also, if the POCO does upgrade us to "true" 3-phase service, will we still be able to run our 120V panel off one of the 3 hot legs?
Any input on this problem would be greatly appreciated.