Yea! well this one did.:roll:A Weeble Motor. "Weebles wobble but they don't burn up!"![]()
Yea! well this one did.:roll:A Weeble Motor. "Weebles wobble but they don't burn up!"![]()
Lack of maintenance.
Touch?!Don't discourage your fans. After all, imitation is the sincerest form of flattery. :grin:
I asked about the OCPD's and was assured they were correct. I will be checking on Monday. :roll:
Did you mean motor overloads should have protected the motor? Who in their right mind would run a 100 hp motor using a fuse or breaker for motor protection?
An untrained person or persons.Did you mean motor overloads should have protected the motor? Who in their right mind would run a 100 hp motor using a fuse or breaker for motor protection?
An untrained person or persons.
Very few electricians understand exactly what it is the o/l s do. Sad but true.Now that is the other matter with untrained or non qualifed dolts they will find a way to oversize the fuse or find a way to increase size of the breaker way above what the NEC called for.
With proper sized fuse or breaker it will serve as back up in case the O/L failure { it happend once a while like that }
Merci,Marc
I have commonly see incompetent persons install the wrong ols. It doesnt phase me anymore. When you are done horsing around with the untrained and have done enough damage I will come in and fix it but it wont be cheap. Many motor driven loads never reach max output so many bad installs get a free ride just by dumb luck.I have see them used for back up only if the standard OL system fail the fuse or breaker should be a back up source but not always the case depending on how you set up system is especally with multi motor set up that will compound it.
Merci,Marc
Did you mean motor overloads should have protected the motor? Who in their right mind would run a 100 hp motor using a fuse or breaker for motor protection?
I don't think you can necessarily infer that.To me it looks like a case of the OCPD set improperly. If set right you should never get motor damage. I bet the breaker tripped at some point from the increased current drawn by the increased friction of the bearings drying out and the electician just turned up the trip setting allowing for the motor to run to failure. Classic case of improper device settings and/or unqualified personel adjusting OCPD's.
To me it looks like a case of the OCPD set improperly. If set right you should never get motor damage. I bet the breaker tripped at some point from the increased current drawn by the increased friction of the bearings drying out and the electrician just turned up the trip setting allowing for the motor to run to failure. Classic case of improper device settings and/or unqualified personnel adjusting OCPD's.
Boy you'd think somone would have noticed the smoke before she blew!
Overtightening the belts might not reflect very much in the motor current. You aren't asking the motor to produce more torque. The torque is proportional to the difference between the two sides of the belt rather than their absolute values so you could over tension the belt to an extent that would be detrimental to bearing life without overloading the motor.Pretty sure the electrician and an amp meter weren't included when these belts were tightened up.
Yea the extra side loading of the bearing proabably would not show enough increase for an installer to notice.Overtightening the belts might not reflect very much in the motor current. You aren't asking the motor to produce more torque. The torque is proportional to the difference between the two sides of the belt rather than their absolute values so you could over tension the belt to an extent that would be detrimental to bearing life without overloading the motor.
I think your asking a lot of the motor OCPDs and just trying to throw stones at at the installer here.
To work like your suggesting the motor would have to be running nearly fully loaded normally to be able for the OCPDs to 'notice' the increased friction of a dry bearing.
Most times motors are not running fully loaded so the increased friction of the bearing would go unnoticed.