To my mind, the biggest practical concern would be if the pigtail from the wire nut to the neutral bar was sized small enough that it might be mistaken for a single circuit neutral by someone who disconnects it without first verifying that all of the breakers feeding a wire in the nut have been turned off.
It also seems similar in some ways to the prohibited practice of putting two neutrals into one terminal on the neutral bar. In that scenario, even though the terminals may be rated for two wires, it is not allowed because removing a single neutral from the termination would at the same time interfere with the connection of the second neutral.
It also seems similar in some ways to the prohibited practice of putting two neutrals into one terminal on the neutral bar. In that scenario, even though the terminals may be rated for two wires, it is not allowed because removing a single neutral from the termination would at the same time interfere with the connection of the second neutral.