al hildenbrand
Senior Member
- Location
- Minnesota
- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
So reading 300.13(B) a little more closely, I see that the wording is ambiguous. You could read it as referring to ((continuity within the MWBC) of the grounded conductor) or as (continuity of the grounded conductor) within the MWBC). In the former reading, the receptacle doesn't need pigtailing, as it is at the end of the MWBC, at least for the usual reading of the definition of MWBC, so if you interrupt the grounded conductor there, the grounded conductor is still continuous within the MWBC. Under the latter reading, which I hadn't previously considered, the device needs pigtailing.

300.13(B) speaks about the continuity of the grounded conductor being interrupted by the removal of a device. . . If the grounded conductor OF THE MWBC lands only on the duplex receptacle terminals, removal of the duplex receptacle WILL interrupt the continuity "of the grounded conductor."