- Licensed Electrician
The Mike Holt graphic shows pigtailing required at the last device on the MWBC when both ungrounded conductors are extended further as part of 2-wire circuits. And the hazard there is real, in that the 120V devices on the 2-wire circuits could be exposed to overvoltage on loss of the neutral. Thus we should interpret 310.13(B) to require that pigtailing.
In the OP's case, where only one ungrounded conductor is extended beyond the last device on the MWBC, the hazard is not present. But the language of 300.13(B) doesn't have anything in it which would distinguish this case from the Mike Holt graphic. So I would say pigtailing is required by the NEC but unnecessary by the physics.
Cheers, Wayne
If you remove the device and nothing bad happens downstream then the wiring is code compliant.