brycenesbitt
- United States
We have seven crufty and jam-prone FPE unit main breakers on a six unit apartment.
There is no capacity problem, just the jamming breaker risk. These are two circuit apartments with
no interior sub-panel.
The proposal was a like for like swap of the panels below the meter bases to resolve the breaker jamming
risk.
The correction came back
Is it reasonable to attempt to comply with NEC 110.9 and NEC 110.10 in a like for like replacement situation ?
risk.
Provide series rated or engineer rated electrical design system. When modifications to
the electrical installation occur that affect the maximum available fault current at the
service, the maximum available fault current shall be verified or recalculated as
necessary to ensure the service equipment ratings are sufficient for the maximum
available fault current at the line terminals of the equipment [NEC/CEC 110.24.B]