Other than 334.12 (A) (10) (b) & (d) are there any other violations that you can see from the attached pictures.
Thank you,
Bernard
Thank you,
Bernard
Other than 334.12 (A) (10) (b) & (d) are there any other violations that you can see from the attached pictures.
Thank you,
Bernard
Other than 334.12 (A) (10) (b) & (d) are there any other violations that you can see from the attached pictures.
Thank you,
Bernard
My eyes must be shot as I can't figure anything out. Looks like 2 whites and a black coming into a T-11 box (bell box). The insulation obviously is not in site so there is an issue with that.
I would question whether or not the UF is subject to physical damage. Heck it is behind the units and not likely to get damaged, IMO. SE cable is more exposed then that and the insulation is not as tough as UF.
Not sure what the mess is under the bell box.
I would never do it either. Carflex is my choice but they say that is not protection from damage either. Weedeater will eat right thru that stuff also.Although I agree,,,there is not an inspector around here that passes UF going to outdoor units. They are suject to weedeater damage.
I would never do it either. Carflex is my choice but they say that is not protection from damage either. Weedeater will eat right thru that stuff also.
AThey are suject to weedeater damage.
Weedeater will eat right thru that stuff also.
What kind of weedeaters do you guys use?![]()
I have also heard that the weedeater can cut the #6 to the ground rod. I would like to see that.
is that romex clamp rated for the location?
I always thought if it were on the bottom it was fine.
How do you keep the cable from unraveling? Silver solder? Small crimp ferrule?:grin: Me too.
I don't think I could do that even when I run aircraft cable instead of nylon line in my trimmer.![]()
Agreed. That's kind of where I was going with "specific wiring method article", but sloppily, I admit.I think the bigger problem are many NM connectors are labeled 'dry location only'.
I might argue under the switch is not a wet location but it is certainly a damp location.
Much of the UF available is rated sunlight-resistant. I actually would trust that to survive better that SE with the same rating.The UF cable 340.12.9