fmtjfw
- Fairmont, WV, USA
I'm not sure this fits the definition of a dwelling unit. There are future provisions of a sanitary pump but not installed. There are future provisions of heat but not permanent. By definition of a dwelling unit you need permanent provisions for sanitation, cooking, living, and sleeping. I would argue that the sanitation and living are not permanent because the lift station is missing and the heat is not permanently installed.I'm wiring a small summer camp for a relative. Are there any suggestions you might have for the design?
because it is not a dwelling unit you cannot derate the neutral.
The deration of the service neutral might need to be full size because the loads cannot be described and because it is not a dwelling unit you cannot derate the neutral. You are also going to have to revisit sizing of the service conductors and take them from table 310.15 B 16 and not 310.15 B 7 Which would lead to re sizing your conduit.
The added panels and the over sized service for a 560 sq ft bld is way over kill. I can see the 200 amp service to facilitate the future needs of say other camp sites but putting in panels where "campers" can access them would be a mistake. The PVC might not hold up to varmints and you should consider steel installation of everything. Cabins have a tendency to get vandalized. Hardening the installation and providing steel conduit will cut down on re installation of the wiring. Since it is not a dwelling unit by definition you wont need arc fault circuits. I would use GFCI breakers on everything and idiot proof the installation. I would also consider using 10 foot ground rods or maybe salting the grounding sites. If its in the mountains rock and no groundwater would make for a high impedance earth ground, you might also consider doing the water bond if there is water to the cabin or a well.
Yes this would add to the cost. 200 amps on a 560 sq ft cabin, not exactly ruffing it, huh?
There is no common sewer, each residence has its own solution. The matter of sanitation is unsettled because the current system is clearly illegal (a pit, leaking into the creek). They are investigating: 1) Aerator/grinder pump system, 2) septic and drain field (unlikely due to rock just below surface in many places and usable 270 X 110 down to 45 quadrilateral lot bordered on one side by creek, and 3) store and pump system.
I do not understand this comment. :?
Sewer lines and septic systems are a scam to limit residential buildings to places where there is a sewer line or a large footprint of land with dry, high perc soil, which is not everywhere. Residential sewage is very easy to treat and results in mostly biofertilizer. Sewage, food, and humans are permutations of the same basic elements. Industrial wastes, solvents, and metals are the hard to treat waste that a plant is needed for.
Your application, you should look at aerated tanks, residential treatment systems like a FAST system. First tank is anaerobic digestion, next tank is an aerobic digestor, then the effluent can be dropped straight into the topsoil. Next step up are membrane bioreactors for really difficult and tight applications. Residential treatment systems are very simple tech, like rotating biological contactors.
If the regulations would allow it you could have a three pipe system. Raw urine is straight fertilizer with low biological hazard, it can go straight to the plant root materials untreated. Grey water, (laundry, kitchen, showers), can go straight to a mulch bed usually around a large tree base.The mulch holds the soaps and detergents for breakdown by microbes. Key is to have a dry aerated layer between the treatment layer and the natural groundwater (sand, fabric, mulch). Solids sewage has the biological hazard but is easily treated and the quantity is a lot less if you are separating out the grey water. They make composting toilets which may work for a camp or a smaller aerated tank treatment system like a FAST. Septic systems are 1000 year old obsolete technology, but the regs are used to limit or make building illegal.
http://www.biomicrobics.com/
They are pretty much dead set against composting toilets.
In your design, ...I did not see anything mentioned about submitting the plans to the"Please critic the attached summer camp design:
I'm wiring a small summer camp for a relative.....Are there any suggestions you might have for the design?"
local AHJ for a plan review and obtaining a permit [ i.e. - let the AHJ determine
if it is a Residential or Commercial application ].......This is a building code determination,
and not an electrical code one !