Maybe you should try actually reading the GPC Blue Book instead of spouting off.you guys are showing me poco sketches from your areas.
they don't apply here, as GPC has no such wording in their blue book which is what we go by. They hooked us up...no prob.
I still have seen only one reply that gave any kind of a code reference, and I greatly appreciate that one. that's what I was looking for, not opinions and design sketches from 1000 miles away.
From GPC's Blue Book section 6.A.3:
"At the point that the service mast conduit passes upward through a roof overhang, at its soffit or through any enclosed fascia area, the service mast conduit shall be one continuous section, with no conduit couplings. All couplings used below the roof overhang or fascia shall be visible in the service mast conduit. No conduit coupling shall be a part of the service mast conduit at any point above the roofline of the building."
add: in case you are having difficulty quoting from a book you haven't thoroughly read:
https://customerservice.southerncompany.com/PDF/BlueBook.pdf