We are installing a ceiling mounted projector using a Da-Lite mfg product specified for plenum use. This device is NOT UL listed. The mfg lists this product as housing an electrician installed handy box with receptacle. The cord from the projector is run through the 1 1/2" NPT mounting pipe directly into the plenum box which is an integral assembly with the projector mount, and then plugs into the provided receptacle.
The local inspector indicates that this is not in compliance with code and cites the NEC 400.8 item 5. He also indicates that the installation might be acceptable if the plenum box/mounting assembly wer to be UL approved. The mfg vehemently declares that the configuration is in compliance with code and UL approval is not required. We are in the middle.
I have two questions: 1. Is the inspector is correct that this is not an acceptable installation? 2. Is there another way to configure this where we do not have to have the receptacle exposed to the room on the ceiling side?
Any help leading us to a better cleaner installation will be appreciated. Jim
The local inspector indicates that this is not in compliance with code and cites the NEC 400.8 item 5. He also indicates that the installation might be acceptable if the plenum box/mounting assembly wer to be UL approved. The mfg vehemently declares that the configuration is in compliance with code and UL approval is not required. We are in the middle.
I have two questions: 1. Is the inspector is correct that this is not an acceptable installation? 2. Is there another way to configure this where we do not have to have the receptacle exposed to the room on the ceiling side?
Any help leading us to a better cleaner installation will be appreciated. Jim