Check these out....
http://www.draperinc.com/Lifts_Mounts_Brackets/VideoProjector_Lifts.htm
http://www.draperinc.com/Lifts_Mounts_Brackets/VideoProjector_Lifts.htm
e57 said:However the reasoning - and I am now stepping into very deep water here - ceilings of the plenum flavor serve as environmental air for the HVAC system,
realolman said:How about a metal enclosure installed up into the ceiling, isolating it's own interior from the plenum, containing a hard wired receptacle for the projector, in a similar manner as a bathroom exhaust fan motor plugs into the receptacle in it's enclosure?
Code compliant or not, this idea makes for a good, long sentence.:smile:
realolman said:Like this... it doesn't go through the ceiling tile any more
e57 said:Soundcon, what I think you are looking for in appearance is available in the floor..... Get one for the ceiling approved and you got a market....![]()
However the reasoning - and I am now stepping into very deep water here - ceilings of the plenum flavor serve as environmental air for the HVAC system, and thus become part of the breathable air in a building when the worst happens. i.e. Fire.... And the propose of not allowing flexible cords in that area above the ceiling is to limit smoke, and fire travel on combustible materials. e.g. Plenum rated Cat-5 cabling is both lower in toxic smoke when burning, and has a lower rate of flame travel by UL testing. The chemical compounds in just about all flexible cords that make them 'flexible' are not produced in a way that could qualify as 'low smoke or flame spread'.... The NFPA and UL are not looking to add any more load to that type of area where it would be both concealed, more prone to fire, and be more toxic, and be inside essentially part of the duct work.... And as Iwire mentioned - the NEC does not want to open the pandora's box of allowing cords being used as premise wiring, as not only are the life-spans of said cordage lower, but the installation of said would then allow many other nasties into the pool - next thing you know we'll be using the non-methods of the hack.... cords to flying splices in walls - whole buildings wired in lamp cord with various voltages and we soon become Bangladesh.....
realolman said:Or this..... ...
![]()
iwire said:I agree, but it is still above the ceiling.
That would be a violation of 400.8(5).
For the above to be compliant someone has to put in a code proposal for a change.
e57 said:After reading the spec sheets for a few related items, I do not see them as implying that - did they provide you with that drawing????
iwire said:That works and many projector mounts come with a spot to do just that.![]()
realolman said:Granted it is a higher elevation, but I do not think it is above the ceiling.
Can you not use any cords at a higher elevation than the lowest suspended ceiling?
iwire said:You want to split hairs all day long we can I got time,:smile: but out on the job it costs real money.
If the inspector sees a power cord going up through a hole into the 'ceiling' it is likely going to be a problem.
Change the code or change the problem but as it is presented here IMO it is a very clear violation.
Perhaps the projector manufacturers could start providing a way to hard wire the units cleanly?
walkerj said:I don't understand why you cant just cut an outlet into the ceiling tile:-?
I think you guys are overthinking this or I'm confused
walkerj said:I don't understand why you cant just cut an outlet into the ceiling tile:-?
I think you guys are overthinking this or I'm confused
stickboy1375 said:I'm confused also, what on earth is so hard about having the receptacle installed next to the projector?
If it (the drawing you posted) came from them - they need new tech support - not the one in Bangladesh.... Or you may be you may have misunderstood, as there would be a 1G metal cut-in box inside the plenum cover - but installed in the method shown by realolman....soundcon said:It may have been a verbal conversation or some such process of determining the application. I may have assumed I could do this and Da-Lite may not have implied anything. However, what is the point of the receptacle (clearly shown in their drawing) in the plenum box if not for plugging in the projector and power supply for a low voltage device.
stickboy1375 said:I'm confused also, what on earth is so hard about having the receptacle installed next to the projector?