update
update
ok guys (or girls) once again......this is portable industrial equipment.....its a standalone mixer with a pump, heater and misc equipment (think of it as a skid on wheels).
Each piece of equipment has its own disconnect as well as fusing and circuit breakers. So no, I can't force feed 60a into the equipment.
There is a tag on the equipment indicating the voltage, phases, and amperage of the equipment. No maximum ampacity circuit call out.
On the one in question, it has cord (15ft?) and a 30a 5 pin plug, 3ph, ground and neutral. The neutral is terminated at the machine but not used past the termination point. Its a standard connector for the manufacturer and allows them to use the same plug as needed for the equipment requirements. This particular piece only requires 480vac, 3ph, 60hz, and the ground.
There is no specific call out for the supply circuit in the manual.
On the wall there is a Hubbel 60a receptacle. Customer requested that I replace the 5pin 30a plug with a 60a unit (without a neutral). NO!!! The neutral is not used at the machine....not now....not ever.....its not there for future additions or expansion.
And its a used piece of equipment that originated in Europe. So even if I could contact the manufacturer, they probably don't have a good grasp of the code requirements in the US.
So is it legal to have a 60a plug on a 30a rated cord, feeding a piece of machinery thats protected at 30a?
thanks, bob:?